Guy I work with asked me if we had 208 power available. As I have wired most of our shop tools I was only aware of 220 1ph. Or 220 3ph. So I told him no 208. He is looking for a UPS for our server.
Later he tells me he thinks 208 is using the two 110 legs, like you would find on a 220 line but to each other instead of the neutral.
Does this seem correct? I’m not seeing it.
Thx.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,241
Location
Modesto, CA
Guy I work with asked me if we had 208 power available. As I have wired most of our shop tools I was only aware of 220 1ph. Or 220 3ph. So I told him no 208. He is looking for a UPS for our server.
there is no 220v in the US. its either 208v, 240v or 480v.... when spec'ing equipment its important to use the correct voltage rating...
Later he tells me he thinks 208 is using the two 110 legs, like you would find on a 220 line but to each other instead of the neutral.
Does this seem correct? I’m not seeing it.
Thx.
not quite

208v is derived from a 208Y/120 3 phase service. you can have 208v single phase, where you only have 2 ungrounded conductors and a neutral from a 208Y/120 3 phase connected transformer....
 
Last edited:

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,322
Location
Dutzow Missouri
I would not be surprised if your building had 208 volt service if is large was built after 1980.

Post a photo of the panel with the 120 volt breaks.

If the panel has a mix of single phase and 3 phase breakers the service will be 208 or 240 high leg.

A high leg panel will have 1 unusable slot for every 2 120 breaker.



Walta
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,366
Location
Coastal NJ
We had 208Y/120v service in our building at work. Sometimes specialized equipment requiring 240 single phase was ordered (by some uninformed folks.) The company electricians would have a fit. They would end up installing a step up transformer to go from 208 to 240.
 
OP
N

no704

Well-known member
Joined
Apr 27, 2016
Messages
5,271
Hmm, now I question myself. It’s been a couple years since I wired any thing here. Panels can take a single, double or triple breaker. For 120, 240 or 240 3 ph as I recall. I’ll get a pic tomorrow.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,877
Location
NW Iowa
Do you have 1 pole breakers that skip every 3rd space? A separate panel that only has 1 phase in it? These are good signs that you have a 240v delta service.

If you can get 120v from any of the 3 phases then you have 208Y
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,128
Location
Central Iowa
Hmm, now I question myself. It’s been a couple years since I wired any thing here. Panels can take a single, double or triple breaker. For 120, 240 or 240 3 ph as I recall. I’ll get a pic tomorrow.
A picture might verify that you have three phase power, but that's it. Unless there is a picture of a meter testing line to line, nobody will be able to tell you what the voltage is. It's either 240 or 208.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,322
Location
Dutzow Missouri
I agree 208 Volts

You may want to check the tags on the equipment connected to the 2 and 3 pole breakers and make sure they are rated to operate on 208.





Walta
 
OP
N

no704

Well-known member
Joined
Apr 27, 2016
Messages
5,271
I agree 208 Volts

You may want to check the tags on the equipment connected to the 2 and 3 pole breakers and make sure they are rated to operate on 208.



Been running a couple years. I’m sure I checked when I wired them.
Just made more work for me! Thanks.

Most of it is 3 ph.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,322
Location
Dutzow Missouri
Yes, it has been working for some time but it seems the person installing the equipment was confused about what voltage was being supplied to the equipment and without that knowledge he might not have noticed a tag that says 240 volts as apposed that says 208\240.

Yes, the 3 phase equipment needs to be checked also because it can be labeled 240 volt only.

Sorry about the extra work.

Walta
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
I agree 208 Volts

You may want to check the tags on the equipment connected to the 2 and 3 pole breakers and make sure they are rated to operate on 208.





Walta
That is a non issue, the 1 & 2 pole breakers normally are rated 120/240V, and any phase is 120V to N, so it does not exceed the lower voltage. It is only a issue with 120/240V 3Ø when the high leg & another phase is used for 240V single phase loads, a 240V rated breaker is required, they are uncommon & expensive,
 
OP
N

no704

Well-known member
Joined
Apr 27, 2016
Messages
5,271
Thanks all. I will double check voltages got the equipment.
 