Alright i don't have pictures to explain but i have a sub panel in my detached garage that appears to have the incoming wires coming into a dual 60 amp breaker then after that there 4 empty spaces and next to that is a single 15 that has my light and outlet ran off of it.

so i'm wondering am i good to add in a dual 20 amp for my 220 and use Romex 10-2 to run it to a outlet behind my new compressor.
 
To avoid these ads, REGISTER NOW!

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
Sight unseen, but given as you describe it, the answer should be yes. Just make sure the in infeed is properly sized for 60A.
 
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
i believe it is, it was installed by a licenses electrician and was approved with a county permit when don't and the wire feeding the 60 amp breaker is a big wire!
 
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
It's 7.5 I believe. I just went with 20amp because the guy I got it from had a electrician wire it in and he use 20 amp and the guy said he never had a problem with it
 

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN
You need to tell us the HP of the motor and the amps on the motor. If it is a true 7.5 HP then it will need to be wired for 50A, so #8 THHN (in conduit) or #6 NM-b (Romex). If he was running on a 20A before it is more like 3HP with some fake advertising.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
It's 7.5 I believe. I just went with 20amp because the guy I got it from had a electrician wire it in and he use 20 amp and the guy said he never had a problem with it

No way would a true 7.5HP motor run on a 20a breaker without tripping it. FLC is 40a.
 
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
It could be 5hp then. It says both on it and I didn't to close attention to it. I just checked the CFM to meet my needs and it did
 
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
Well I can't look at the tag right now but looked up the new version of my compressor that's offered and they rate it at 24 amps. Do I go 30 or do I need bigger
 
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
Is this bar acting as both the ground and the neutral bar?
Or in simple terms am I ok to wire my ground (green) into this bar
 

Attachments

  • IMG_0221.jpg
    IMG_0221.jpg
    137.9 KB · Views: 30

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
Or in simple terms am I ok to wire my ground (green) into this bar

No, not on a sub panel. You will need a hold down kit for back-fed 60A feed, and a ground bar which will be bonded to the chassis.

The ground and the neutral are only connected at the service entrance of the house.
 
To avoid these ads, REGISTER NOW!
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
Are you able to link me to this hold down kit or something. I have no idea what that is. As for the ground bar where would I install that
 

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
I guess I should back up a second. I am assuming that the neutral bus is not bonded to the chassis, that is how it appears. But with the wires disconnected from the bus, and the power off, you should check for continuity between the bus and the ground.
 

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
Use this type of bus if there is in fact continuity between the existing bus and the chassis, and now land all your neutrals here
 

Attachments

  • Screen Shot 2016-10-06 at 9.43.56 AM.jpg
    Screen Shot 2016-10-06 at 9.43.56 AM.jpg
    4.8 KB · Views: 14

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
If the existing bus is in fact isolated from the cans chassis, the leave the neutrals there and land the ground wires on a bus like this, installed solidly to the can by yourself in a convient location.
 

Attachments

  • Screen Shot 2016-10-06 at 9.43.44 AM.jpg
    Screen Shot 2016-10-06 at 9.43.44 AM.jpg
    4.1 KB · Views: 10

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
A hold down will look something like this, and be made specific for you panel and breakers
 

Attachments

  • Screen Shot 2016-10-06 at 9.40.05 AM.jpg
    Screen Shot 2016-10-06 at 9.40.05 AM.jpg
    6.6 KB · Views: 10
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
Alright it looks as if the neutral bond screw has been removed. I looked up the model of my box and it talks about removing that binding screw and it's gone.
So now I found the part number for the ground bus but how do I ground it? Do I just move the ground coming from the house over to that bar?
 

bobmulry

Well-known member
Joined
Nov 21, 2012
Messages
144
Location
Coarsegold, CA
Is this bar acting as both the ground and the neutral bar?
Or in simple terms am I ok to wire my ground (green) into this bar

Looking at your box it seems that they only pulled 2 hots and a neutral but no ground????????????????????????????????

I thought that you would need a dedicated equipment ground with a separate neutral & ground buss bar (not tied together)

Bob
 
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
There 4 wires coming in. Black and red going to the 60 amp breaker and a white going to that top right post and then the green wire going to the bus bar.
I think the green is the ground?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
It could be 5hp then. It says both on it and I didn't to close attention to it. I just checked the CFM to meet my needs and it did

Well I can't look at the tag right now but looked up the new version of my compressor that's offered and they rate it at 24 amps. Do I go 30 or do I need bigger

That would be a 5HP motor. 5HP FLC is 28a.

A 20a circuit is too small for that.

Need #10 THWN in pipe or #8/2 NM-b. Disconnect is required if not within sight of panel and further than 50'.

Is this bar acting as both the ground and the neutral bar?
Or in simple terms am I ok to wire my ground (green) into this bar

That panel is setup incorrectly. Whoever wired it didnt know what they were doing.

Heres a pic:

491611d1439733610-grounding-implications-3-wire-feeder-subpanel-detached-garage-4-wire-feeder.jpg


Its 4-wire fed and Neutral bar is isolated but the EGC/ground wire(green) is going to the same bar. This wire should be on a separate bar screwed directly into the panel. All ground wires should be on this new bar.

And as has been mentioned, that main breaker, needs to have a hold down screw/kit.

However, u will have 6 or less breaker handles so a main breaker isnt required. They are nice to have though.

Alright it looks as if the neutral bond screw has been removed. I looked up the model of my box and it talks about removing that binding screw and it's gone.
So now I found the part number for the ground bus but how do I ground it? Do I just move the ground coming from the house over to that bar?

Yes move the green wire over to this new bar.

There should be some prepunched holes in the can. U use the self taper screws that come with the bar to mount it.

U also need 2 ground rods.

There 4 wires coming in. Black and red going to the 60 amp breaker and a white going to that top right post and then the green wire going to the bus bar.
I think the green is the ground?

Correct. Read above
 
OP
E

egobuster1

Member
Joined
Apr 23, 2016
Messages
15
Yeah I'm getting the ground bar and the grounding rod and gonna move the grounds over and put in the new 30 amp breaker
 

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
Wylie is a real electrician, and you should always do exactly what they say if their advice is even slightly contrary to a non electrician like myself.
 