It could be 5hp then. It says both on it and I didn't to close attention to it. I just checked the CFM to meet my needs and it did
Well I can't look at the tag right now but looked up the new version of my compressor that's offered and they rate it at 24 amps. Do I go 30 or do I need bigger
That would be a 5HP motor. 5HP FLC is 28a.
A 20a circuit is too small for that.
Need #10 THWN in pipe or #8/2 NM-b. Disconnect is required if not within sight of panel and further than 50'.
Is this bar acting as both the ground and the neutral bar?
Or in simple terms am I ok to wire my ground (green) into this bar
That panel is setup incorrectly. Whoever wired it didnt know what they were doing.
Heres a pic:
Its 4-wire fed and Neutral bar is isolated but the EGC/ground wire(green) is going to the same bar. This wire should be on a separate bar screwed directly into the panel. All ground wires should be on this new bar.
And as has been mentioned, that main breaker, needs to have a hold down screw/kit.
However, u will have 6 or less breaker handles so a main breaker isnt required. They are nice to have though.
Alright it looks as if the neutral bond screw has been removed. I looked up the model of my box and it talks about removing that binding screw and it's gone.
So now I found the part number for the ground bus but how do I ground it? Do I just move the ground coming from the house over to that bar?
Yes move the green wire over to this new bar.
There should be some prepunched holes in the can. U use the self taper screws that come with the bar to mount it.
U also need 2 ground rods.
There 4 wires coming in. Black and red going to the 60 amp breaker and a white going to that top right post and then the green wire going to the bus bar.
I think the green is the ground?
Correct. Read above