220 off a single pull 20amp

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
After reading all this information I'm sure glad I tested that outlet and realized something I was messing with was more then I knew. The more I think about it I almost want to hire someone to put in a new single phase panel.

Don’t do that! You have three-phase distribution. This is a diamond in the rough. You’re probably already paying for it and don’t know about it.

Give your test metre a 10 minute workout and come back with the results...
 
Last edited:
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Note: Any 2 pole used on the high leg & any other phase MUST be rated for 240 volts, standard 120/240V breakers cannot be used, there plenty of space so it is not a issue, straight 240V breakers are very expensive & uncommon.


This thread is just another reason why people who think 110, 220, volts still is used should not do any electrical, knowing the nominal voltages one is working on is important
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,581
I have a similar installation in my home shop. It is separate from my home on its own service/meter. It is my understanding that the high leg should be Orange, not red, by current code.
In my case, I have the 3phase panel as the main and a smaller single phase fed from that. Mine came about because the original single phase service main breaker failed and I added the 3phase instead of just replacing the main breaker. I lucked into a really cheap panel loaded with breakers and my provider installed the added wire and transformer at no charge. I needed it for my compressor and table saw. Well, I didn't strictly need it, as I could have bought single phase motors, but would have cost much more.

But, it is a good solution that can prevent accidentally grabbing the wrong open slot. Just use one panel for single phase loads and the other for 3ph.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
I It is my understanding that the high leg should be Orange, not red, by current code.


Although it's sometimes called a "Red Leg Delta", the high leg is required to be Orange, NEC 110.15 and on the "B"Ø.(except for San Francisco, where it's required to be purple)
Power Companies generally supply it as the "C" leg, because of metering issues.
The electrician is responsible for swapping them in the first place possible beyond the meter.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,735
Location
NW Iowa
After reading all this information I'm sure glad I tested that outlet and realized something I was messing with was more then I knew. The more I think about it I almost want to hire someone to put in a new single phase panel.

WHY?! Most people on here can only dream of having three phase in their shop.

If working in this panel bothers you that much then install a single phase sub panel next to the old one. Run all your 120v circuits out of the new panel. Normally this is done for extra space, but it also eliminates any confusion and possibility of a 120v circuit being placed on the high leg.
 
OP
N

Need more space

Well-known member
Joined
Jun 23, 2014
Messages
253
Location
Michigan
Don’t do that! You have three-phase distribution. This is a diamond in the rough. You’re probably already paying for it and don’t know about it.

Give your test metre a 10 minute workout and come back with the results...

Paying for it as in the price of the shop?
 
OP
N

Need more space

Well-known member
Joined
Jun 23, 2014
Messages
253
Location
Michigan
WHY?! Most people on here can only dream of having three phase in their shop.

If working in this panel bothers you that much then install a single phase sub panel next to the old one. Run all your 120v circuits out of the new panel. Normally this is done for extra space, but it also eliminates any confusion and possibility of a 120v circuit being placed on the high leg.

I guess I never thought of it that way, I just currently have no need for it so I didn't really see its value. I'm just happy there's room to wire my hoist and compressor when it shows up.
 
OP
N

Need more space

Well-known member
Joined
Jun 23, 2014
Messages
253
Location
Michigan
You have a three-phase system. It should be 120/208/120

The main breaker is the top left and they’re all tied together. There is three different hit’s coming in.

L2 should be your 208 to neutral. But just in case it’s not...

Test:
L1 to L2=243
L1 to neutral=120
L2 to L3=247
L2 to neutral=122
L3 to L1=247
L3 to neutral=206

And let us know what your numbers are.

Results above
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,735
Location
NW Iowa
I guess I never thought of it that way, I just currently have no need for it so I didn't really see its value. I'm just happy there's room to wire my hoist and compressor when it shows up.

It really opens up your options for machinery. Lot's of used industrial machinery, air compressors, lathes, mills, welders, grinders, ect are 3 phase. This stuff is often dirt cheap for high quality equipment because many homeowner types can't run them.
 

GRB

Well-known member
Joined
May 6, 2014
Messages
828
Location
SoCal
Results above
Three phase Delta with the hot leg on C (or L3).

You can put a three pole (three phase) breaker anywhere. Two pole (240v) anywhere. Single pole (120v) in #1, #2, #4, #5, #7, #8, etc. NOT #3, #6, #9 etc. NOT the third slot and in every third slot after that.

Simply fabulous if you have that in a residential area. I would be thrilled.
 

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
Test:
L1 to L2=243
L1 to neutral=120
L2 to L3=247
L2 to neutral=122
L3 to L1=247
L3 to neutral=206
Results above

Results above

Those all look pretty good to me. And your high leg is L3, like I kind of assumed. It should really be put on the centre. Those are your six different voltages and three different phases.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
The Union Electrician Neighbor is incompetent on this system. The "High leg" is clearly Phase C on this system which was the norm on earlier systems. They switched to Phase B in the late 1970s or 1980s depending on the area.
The "Hot Leg" aka "High Leg" feed should be marked with red tape where it comes in but the obvious give away is the every-third-breaker-slot blanking plate starting with #3.
Since there isn't an actual transformer pot on the hi leg, you should NOT use it for any single pole breakers even if you could get a single pole breaker rated for 208v, which is unlikely. That means a breaker that says 208v or more, NOT 120/240v. The POCO tell you in general to NOT use it anyway.
A 3 phase breaker goes across all three obviously. A normal 2 pole 240v can go across any two as long as you don't use the neutral for that load since one side is 120v and the other is 208v. Single pole 120v can go anywhere except in the third slot and every third after that such as #3, #6, #9, etc.

Ive had guys tell me theyve used the hi leg for 208v loads line to neutral. I always thought it was a bad idea. What is the reasoning why it shouldnt? Because there isnt a transformer coil for it? Why does that matter?

And straight rated breakers ARE available, albeit pricey. They were mainly used for corner grounded delta systems.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Ive had guys tell me theyve used the hi leg for 208v loads line to neutral. I always thought it was a bad idea. What is the reasoning why it shouldnt? Because there isnt a transformer coil for it? Why does that matter?

And straight rated breakers ARE available, albeit pricey. They were mainly used for corner grounded delta systems.

There are no single pole breakers made for loadcenters that are rated for 240V, could use a 480/277V panel & use single pole 277V breakers, it's been done when a higher AIC rating was needed, but the high leg is not intended for L-N loads, but nothing wrong w/ using it & another phase for a straight 240V load as long as the 2-pole breaker was rated for 240V.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
There are no single pole breakers made for loadcenters that are rated for 240V, could use a 480/277V panel & use single pole 277V breakers, it's been done when a higher AIC rating was needed, but the high leg is not intended for L-N loads, but nothing wrong w/ using it & another phase for a straight 240V load as long as the 2-pole breaker was rated for 240V.

Cant get a straight rated single pole breaker for corner grounded delta? I had someone tell me thats what they did...
 

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
Cant get a straight rated single pole breaker for corner grounded delta? I had someone tell me thats what they did...
On the breaker it has to say 1 pole Type, 240-300 v.a.c UL. The external plastic or internal sheathing, heat load has to be rated for that voltage. Each insulation has its own factor. The higher the voltage potential, the higher insulation factor needs to be.

For fun compare A 30 amp 250vac fuse to a 480vac(or 600vac)....
 
Last edited:

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,961
Location
East Cobb County, Georgia
Ive had guys tell me theyve used the hi leg for 208v loads line to neutral. I always thought it was a bad idea. What is the reasoning why it shouldnt? Because there isnt a transformer coil for it? Why does that matter?

And straight rated breakers ARE available, albeit pricey. They were mainly used for corner grounded delta systems.

As I always understood, the neutral is sized for the 2 phases (A & C) that it should carry, but adding B to it can overload the neutral. The maximum imbalance the neutral could carry if nothing were on one phase and the other fully loaded would be equal to the phase current of the other and the neutral wire then is already maxed out. Add any load at all from the third phase and it would be overloaded. I'm sure most installations don't come close to such a situation, especially if there is a good mix of 240V loads, so you can probably get away with it in many cases.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
As I always understood, the neutral is sized for the 2 phases (A & C) that it should carry, but adding B to it can overload the neutral. The maximum imbalance the neutral could carry if nothing were on one phase and the other fully loaded would be equal to the phase current of the other and the neutral wire then is already maxed out. Add any load at all from the third phase and it would be overloaded. I'm sure most installations don't come close to such a situation, especially if there is a good mix of 240V loads, so you can probably get away with it in many cases.

Yeah Ive seen some Delta services with reduced neutrals. But not all of them are.
 
OP
N

Need more space

Well-known member
Joined
Jun 23, 2014
Messages
253
Location
Michigan
Those all look pretty good to me. And your high leg is L3, like I kind of assumed. It should really be put on the centre. Those are your six different voltages and three different phases.

What would be the best way of fixing that ( or just let it be? ) if I'm understanding correctly I would turn power off at meter, then switch the wire or just move the breaker on #2 and #3 of the main braker?
 

GRB

Well-known member
Joined
May 6, 2014
Messages
828
Location
SoCal
I would let it be. It isn't the tiniest bit strange here. Every one of those I've seen have had the high leg on Phase C. If C was the norm where you are, it would be weird to change it.
 

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
Yep, just leave it, (unless you’re having it inspected in the near future) unless you’re required to change it. You now know what you have.

It seems to me that you do not have any three phase requirements. I do and when I go to a plug or outlet, I always like to have the prong opposite of ground being my High leg. It just helps me troubleshoot for coil voltages.
 
Last edited: