alfredeneuman
Well-known member
Which is right in post 20. 60%
All right. I GIVE, uncle!
The multiplier for a 60% duty cycle is .78, which is .02 less than .8
Which is right in post 20. 60%
Here are the specs for the Plasma Cutter. So, any if any experts can advise on the proper gauge wire and circuit breaker amp I'd appreciate it. Thanks alot everyone. Be safe
Funny... I've got #8 wire feeding my 220/230/240 outlet. The wire on my welder's #14.
You got your bases covered.![]()
It means at LEAST the wire listed for it at 30A. It would be 12 for 60%, the 200 migs allow 14. Some comps could use the same circuit but the recept is limited to 3 hp. It would allow all 50A welders on it but other 240 equipment may be circuit breaker limited, not all stuff runs on 240 can be connected to a 50A circuit.The spec sheet pretty much claims that the machine needs 20+ amps. (4.8 kVA input, which is 20-22 amps depending on whether you have 220 or 240V coming in at the machine).
That means that the DEDICATED circuit feeding the plasma cutter needs to be at LEAST a 30 amp circuit.
And depending on the wire length between the breaker/panel and the outlet, that means at LEAST 10 AWG copper wire (unless you attempt to go with some duty-cycle undersizing allowance, but then you have to label that the circuit is DEDICATED to just that piece of duty-cycle limited equipment).
Me? I'd skip the fussing and just go with a 50 amp circuit and #8 AWG copper THHN/THWN (depending on circuit length, you might have to go up to #6 AWG copper) and put a NEMA 6-50 receptacle on it and call it done. This way you can use that plasma cutter or some other one of similar input power requirements, or a choice of decently sized 240V welders, or a decently sized compressor, or almost whatever home-shop 240V equipment you want to run off of that circuit.
Dual voltage plasma cutters (like the CUT-50) will limit input power when operating on 120v. That's why you don't pop any breakers.but anyways... I have run it on a 12Ga 120V 20AMP and never pop a fuse...saying that... don't confuse the output current with the input current.
CUT-50s are decent enough machines, and work quite well when fed with 240V.Sorry to inform you that plasma cutter CUT-50D is a piece of ****...
Dual voltage plasma cutters (like the CUT-50) will limit input power when operating on 120v. That's why you don't pop any breakers.
CUT-50s are decent enough machines, and work quite well when fed with 240V.
sberry:
Notice that I said the rule was for 15A and 20A circuits only.![]()
Sorry to inform you that plasma cutter CUT-50D is a piece of ****... but anyways... I have run it on a 12Ga 120V 20AMP and never pop a fuse...saying that... don't confuse the output current with the input current... seems like a lot of people here seems to think they have a 200Amp welder, they will needed a 2/0 1000 Gazilion amp breaker installed to run it.... weird... but sure.
not sure if it is still true, Canada stills runs 110/208Not sure why... at least the last ElectroVblog guy says so...Don't get your ******* in a bunch....

Funny... I've got #8 wire feeding my 220/230/240 outlet. The wire on my welder's #14.
You got your bases covered.
LOL no you didn't you forgot 208.....

Sorry to inform you that plasma cutter CUT-50D is a piece of ****... but anyways... I have run it on a 12Ga 120V 20AMP and never pop a fuse...saying that... don't confuse the output current with the input current... seems like a lot of people here seems to think they have a 200Amp welder, they will needed a 2/0 1000 Gazilion amp breaker installed to run it.... weird... but sure.
not sure if it is still true, Canada stills runs 110/208Not sure why... at least the last ElectroVblog guy says so...Don't get your ******* in a bunch....
What is the 6-x0R receptacle you mentioned before? I tried researching it but couldn't find it. Thanks
What is the 6-x0R receptacle you mentioned before? I tried researching it but couldn't find it. Thanks
6-x0r could be a 6-30r or a 6-50r, I think he just used the x as a placeholder.
6-50r is the common plug supplied on a lot of welders.
Thanks everyone for the responses. I realize the plasma cutter I'm borrowing isnt the greatest but I have a sheet of steel I dont need and would like to use it instead of just getting rid of it.
Couple questions.
I'll go with 30 amp fuse and 10 gauge wire...I realize 8 gauge may be better but is there a danger with using 10 gauge for this.?
Also, for most of these 250 volt plugs there is no green ground screw (obviously it just utilizes the neutral wire for the ground back from the outlet back to the panel. One of the outlets even said on the back, that it is not designed for grounding the outlet.
My question is why don't those outlets use a green ground ALSO, or at the very least ground it to inside of the metal box like im used to with the regular 120 volt outlets? Thanks. Alot.