I had an electrician wire my garage and I was sheeting it today when a friend pointed out something to me.

I am running 2-220 outlets on 30 amp breakers.
I bought all the wire... At homedepot I asked them for 220 - 30 wire and this is what they gave me. It has 2 thick 110's ? and a ground? But no common??? It's wired into both hot sides of a double wide breaker?:confused:

Sorry I know nothing about electrical... But now my friend has me thinking I'm going to have to open my walls up and run different wire.:mad:



 
To avoid these ads, REGISTER NOW!

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
if the equipment,welder,table saw ect,is a 220 volt device,no neutral is required.an example of equipment needing a neutral would be a cloths dryer.the heating elements are 220 but the motor and display is 110.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
What equipment will u be plugging into these outlets?

Personally, i would always run 4-wire, regardless of needs, in case i ever might need the neutral.
 

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
I wouldn't worry about it now.

You only need the neutral "common" for 120v so for your welder and a/c you should be fine.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
What kind of "electrician" wired that outlet box? I would be looking at everything he has done, and if he worked for me-he would be now looking for a new job.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
What kind of "electrician" wired that outlet box? I would be looking at everything he has done, and if he worked for me-he would be now looking for a new job.

I was gonna say the guy put it on 2 separate single pole breakers lol,or is that a 2 pole tandom setup. I don't see a separation in the middle of the breaker only by the screw area
Not to mention the mc connector and it's backwards,box is screwed to side instead of getting a nail on box,just a couple things I can come up with
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
More than two ground wires under the screw in the ground bar, in the panel. For neutrals its one per screw, grounds its two per screw. This is pretty much the norm as specified by the panel manufacturers. Its a Square D panel.

Box should have been a nail on with flange spot welded to the box for alignment and attachment to the stud. Kinda funky looking device holding the Romex where it passes thru the box. Romex not stripped back far enough, not enough wire (esp the ground) to make a pass around the ground screw in the back of the box and then to the receptacle with lots of slack. I leave enough wire to make a pass all the way around the inside of the box most of the time. This leaves lots of slack to remove or install the receptacle.

I was gonna say the guy put it on 2 separate single pole breakers lol,or is that a 2 pole tandom setup. I don't see a separation in the middle of the breaker only by the screw area
Not to mention the mc connector and it's backwards,box is screwed to side instead of getting a nail on box,just a couple things I can come up with

Square D double pole breakers are one piece body (actually two halves carefully mated together), one handle, not the two single poles riveted together like other brands.

Charles
 
Last edited:
To avoid these ads, REGISTER NOW!

The mean fish

Well-known member
Joined
Aug 31, 2010
Messages
323
Those are quad breakers.

d3313419-7255-4bfe-ad99-e709c07e4583_4.jpg
 

The mean fish

Well-known member
Joined
Aug 31, 2010
Messages
323
Technically the breaker pictured is a Tri-breaker. 2 SP and 1 DP.

Hmmmm, Square D/Homeline and Eaton/CH calls them quad breakers...

http://www.lowes.com/pd_8934-296-HOMT2020230CP_0__?productId=3129819

http://www.homedepot.ca/product/bolt-on-duplex-quad-replacement-breaker-2-1p-15a-1-2p-30a/943154

but that seems to be a regional thing because around here we call them quad breakers unless they're 2 DP with the inner and outer breakers linked, we call those "dual tandem".

ddbec389-b6e4-45f2-ab32-52dd751e35e3_400.jpg


I've never heard anyone call them tri-breakers before, must be a regional thing.
 