To avoid these ads, REGISTER NOW!

220 Volt New sub panel In garage

sidanas

New member
Joined
Sep 29, 2012
Messages
1
Location
TURLOCK CA
I am going to install a 220V 100 Amp sub Panel in garage for my tools which are a saw and air compressor. I run a conduit from Main Panel of two hot wires and a ground . Not Not sure how to use Neutral in sub Panel. Please confirm
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
A 240V sub panel requires 4 wires. 2 hots, neutral and ground. Neutral and ground are separated in the sub-panel. The sub-panel will most likely need a ground bar added for the ground. The neutral goes to the bar already in the sub-panel but you need to remove the bonding screw from the bar to the panel. The neutral needs to be isolated. The neutral is how you get 120V.
 
To avoid these ads, REGISTER NOW!

Ironhorse

Well-known member
Joined
Sep 17, 2012
Messages
800
A 240V sub panel requires 4 wires. 2 hots, neutral and ground. Neutral and ground are separated in the sub-panel. The sub-panel will most likely need a ground bar added for the ground. The neutral goes to the bar already in the sub-panel but you need to remove the bonding screw from the bar to the panel. The neutral needs to be isolated. The neutral is how you get 120V.

Well said...most people miss the removal of the bonding screw...:D
 