I just got the power on in my shop and installed a 30a/220v circuit for my table saw. It's a dedicated circuit, single run of 10-2 romex 40' from the panel to a L6-30 receptacle. I have 110v on each leg but the motor will not run. I took the motor to a motor shop twice, he cleaned the start contact switches but says there's nothing wrong with the motor.
I worked my way back from the saw, wiring the motor directly at each junction until I connected the motor directly to the breaker with a short piece of SO cable and it ran. This made me think I had a break somewhere in the romex so I bought more. Before running the new romex I wired it directly to the breaker like I did with the SO cable, and it will not run. So, it will not run on either 45' piece of romex but it will run on the 8' piece of cable. Any ideas?
I worked my way back from the saw, wiring the motor directly at each junction until I connected the motor directly to the breaker with a short piece of SO cable and it ran. This made me think I had a break somewhere in the romex so I bought more. Before running the new romex I wired it directly to the breaker like I did with the SO cable, and it will not run. So, it will not run on either 45' piece of romex but it will run on the 8' piece of cable. Any ideas?