My 2 post lift motor is a 3 wire & the 220v box has 4 wires. Any guidance would be great. I have the conduit & 10/2 run, just need to terminate at both ends.
Thanks
Thanks
You ran 10-2 romex AND conduit? Why?
The 220 box you mention, is that the panelboard?
Steevo steered you right, the neutral (white), isn't used.
A car lift runs for all of about 30 to 45 seconds, and then it sits. Why waste a good circuit, especially if it is a long run.
Charles
Is Romex okay to use in conduit? I thought it was a no no.
Should get the code book guys, out from behind the woodwork.![]()
This question comes up all the time.
At the risk of angering many (honey, I can't go to bed, someone on the Internet is wrong!), here is my opinion on the matter:
1) Running Romex in Conduit is technically not allowed. Code (and most inspectors) say you should run individual wires made for the purpose in conduit. It is more expensive to use individual wires. There are several theories as to why, the best I know of is that the individual wires must be marked a certain grade. If the individual wires inside Romex aren't marked, it's technically not allowed. I have looked this up in the NEC and it's true. Also, there is an argument that the wires bundled close together will heat up. Some remove the wrapping from Romex and just run the wires. This isn't allowed (again, technically) unless the wires are marked (THHN 90C from memory, that might not be it).
2) Some say that Romex is technically allowed but only in "dry" locations. Inside is considered a dry location. Outside or buried are considered wet locations. I think this is a descent argument.
3) Legal or not, many people run Romex in Conduit. I have run Romex in conduit for my own purposes but never for a customer.
4) It is certainly OK to run Romex in conduit for short runs. A good example of this is between utility boxes, to light fixtures, etc. Runs less that a foot are acceptable by the letter of the NEC.
YMMV, do what you think is right. I haven't seen a good physics argument as to why Romex shouldn't be used in conduit but electricity is dangerous!
Okay you need to cite the NEC code section on this. First off the NEC gives direction on how to calculate the size on multiconductor cable or flexible cord for conduit fill percentage. The issue with Romex (NM) is the marking is on the outer sheathing and not the individual conductors meaning you cannot strip off the sheathing completely and use the individual conductors in conduit.
See 2011 NEC 334.15(B). (Exposed Work, Protection from physical damage). NM cable shall be protected by conduit.
"NEC 310.120 All conductor and cables shall be marked..."
The NEC says each conductor needs to be marked. The way I read this, an outer sheath marking alone is not sufficient.