Since you didn't have the ground connected on the male end you should check the female end to see how it was wired.
 
Last edited:
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,316
Location
NJ
This post has been brewing for a week. Imagine if the cover was taken off the panel and recepts pulled out of the box how much factual info that would yield. :unsure:

........🍿
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,382
Location
Coronado, CA
Because my only 240 circuit is fed from the Main Panel both the Ground and the Neutral are landed on the same Buss Bar. If they came from a Sub Panel they would be landed separatly then I would use a fourth conductor for the neutral.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,977
Because my only 240 circuit is fed from the Main Panel both the Ground and the Neutral are landed on the same Buss Bar. If they came from a Sub Panel they would be landed separatly then I would use a fourth conductor for the neutral.
Ground and neutral are not the same, even though they are connected at the first point of disconnect.
 
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,404
Location
Coastal NJ
Because my only 240 circuit is fed from the Main Panel both the Ground and the Neutral are landed on the same Buss Bar. If they came from a Sub Panel they would be landed separatly then I would use a fourth conductor for the neutral.
What does your 240 circuit feed? Since it's a 240 circuit, you don't need a neutral. A 120/240 circuit needs a neutral. And all of them need a ground. Makes no difference if the source is a sub or a main panel.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,382
Location
Coronado, CA
What does your 240 circuit feed? Since it's a 240 circuit, you don't need a neutral. A 120/240 circuit needs a neutral. And all of them need a ground. Makes no difference if the source is a sub or a main panel.
I have a long cable that I use to power my Arc Welder and Table Saw. The cable has a receptical that can take the plug of either the Welder or Saw, but not both at the same time.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,274
Location
Modesto, CA
Because my only 240 circuit is fed from the Main Panel both the Ground and the Neutral are landed on the same Buss Bar. If they came from a Sub Panel they would be landed separatly then I would use a fourth conductor for the neutral.

Even though neutral is bonded to ground at the main or first means of disconnect, they are vastly different downstream

EGCs/grounding conductors/bond wires do not carry current under normal circumstances…. On the other hand, neutrals/grounded conductors do carry current under normal circumstances.
 