Hoping you guys can spot check something for me.
I got a new Ingersoll Rand SS4L5 230V Standalone Air Compressor. It's got a single phase 5HP motor on it. Here's the nameplate:
https://imgur.com/a/9lEfhKk.jpg
The compressor is located ~40' from the breaker box through walls and ceiling. I'm no NEC expert, but I've been reading through various sections and have come up with the following gameplan:
NEC 430.6 says to use the appropriate table to determine the ampacity of conductors instead of the current rating on the nameplate. Table 430.248 indicates a 5HP motor at 230V has a full load of 28A.
NEC 430.22 says conductors supplying a single motor used in a continuous duty application should have an ampacity not less than 125% of the value determined by 430.6. So in this case, my conductors need to be capable of carrying 28A * 125% = 35A. So it looks like some 8/2 w/g Romex would do the trick here, as that's rated for 40A.
Now, for over current protection. According to NEC 430.32A and C, you can go either 125% OR up to 140% if 125% is too low to get the motor started. Rounding up it looks like a 40A breaker would do the trick for both cases and it matches the conductor rating.
I had planned to run the conductors to the wall behind the compressor, connect to an AC Disconnect (60A), and then use an 8/2 whip to connect from the disconnect to the compressor itself.
Have I forgotten anything? Does my approach seem like it'll work well based of what you guys have witnessed in your own shops?
I got a new Ingersoll Rand SS4L5 230V Standalone Air Compressor. It's got a single phase 5HP motor on it. Here's the nameplate:
https://imgur.com/a/9lEfhKk.jpg
The compressor is located ~40' from the breaker box through walls and ceiling. I'm no NEC expert, but I've been reading through various sections and have come up with the following gameplan:
NEC 430.6 says to use the appropriate table to determine the ampacity of conductors instead of the current rating on the nameplate. Table 430.248 indicates a 5HP motor at 230V has a full load of 28A.
NEC 430.22 says conductors supplying a single motor used in a continuous duty application should have an ampacity not less than 125% of the value determined by 430.6. So in this case, my conductors need to be capable of carrying 28A * 125% = 35A. So it looks like some 8/2 w/g Romex would do the trick here, as that's rated for 40A.
Now, for over current protection. According to NEC 430.32A and C, you can go either 125% OR up to 140% if 125% is too low to get the motor started. Rounding up it looks like a 40A breaker would do the trick for both cases and it matches the conductor rating.
I had planned to run the conductors to the wall behind the compressor, connect to an AC Disconnect (60A), and then use an 8/2 whip to connect from the disconnect to the compressor itself.
Have I forgotten anything? Does my approach seem like it'll work well based of what you guys have witnessed in your own shops?