This is my first post but have been a member for a few years. I would like to finally install an outlet for my hobart 180 mig welder. I was going to use a 30amp breaker with 10-2 wire. How long of a wire run can I go without having any voltage loss? Thanks in advance for the help.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You should be okay up to about 125 ft.

Edit: Oh you said no voltage loss. That would be about 2 feet. :D
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
A 10/30 is an ideal circuit for that machine and a 10 is 2 code sizes bigger than the minimum wire and a size heavier than the cord, as patten said,, a long way before its a worry.
 

troyks

Member
Joined
Aug 27, 2014
Messages
23
Location
Kansas
I have a Hobart 190 on a 30 amp breaker on #10 copper, my run is probably 60-70 feet. I did a voltage drop calculation for mine and at my distance I have around 1% voltage drop @ 21 amps (what the Hobart 190 pulls at full load). Up to 3% voltage loss is generally considered fine, so with the similar welder load you could go up to around 170 feet on #10 and still be fine.
 
To avoid these ads, REGISTER NOW!
OP
R

rangerfx4man

New member
Joined
Sep 5, 2012
Messages
2
Location
Central New York
Thanks everyone for the imput. Usually when I have a question I use the search and can get my answer, but didn't have any luck with this one. My wire run is going to be around 40'. My panel is in the back corner of my 24x24 and I want the welder plug up front between the overhead doors. My garage is unfinished and want to be able to weld out in the driveway so I don't burn the place down.
 

Linkon

Active member
Joined
Feb 2, 2015
Messages
44
I have a Hobart 190 on a 30 amp breaker on #10 copper, my run is probably 60-70 feet. I did a voltage drop calculation for mine and at my distance I have around 1% voltage drop @ 21 amps (what the Hobart 190 pulls at full load). Up to 3% voltage loss is generally considered fine, so with the similar welder load you could go up to around 170 feet on #10 and still be fine.

I have this same welder, same #10 copper wire, 30 amp breaker, and my run is about the 80ft with six outlets. Has been working great for a couple years now.
 