240/120 on same circuit

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
When we run a 3 wire + ground conductor, I see that two hots are used for 240v needs and one hot/neutral is used for 120v needs as the bulb. This is how electric dryers are set up (afaik).

Can the same be done for multiple loads? For example, I was planning to run 30a circuit to gazebo for infrared heater. Can I add lights, fan and outlets on the hot/neutral for 120v? I realize I need to provide GFCI protection for 120v side but wanted to see if one circuit can suffice.

if it is a code violation, can you please explain why?

thanks
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,759
Location
Richmond, VA
You want to put 15 or 20a 120v outlets on a 30a circuit? Yes, that would be a violation without additional over current protection.

A small subpanel sounds like the right answer
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
You want to put 15 or 20a 120v outlets on a 30a circuit? Yes, that would be a violation without additional over current protection.

A small subpanel sounds like the right answer
Thank you! Simple but elegant explanation…
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,454
Location
Northern Virginia
But to the OP’s example/question, the 120V light bulb in the dryer is being fed from (likely) a 30A 240V breaker. How is this then safely done? Or do we just look away since the dryer is a UL listed device (black box)?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
But to the OP’s example/question, the 120V light bulb in the dryer is being fed from (likely) a 30A 240V breaker. How is this then safely done? Or do we just look away since the dryer is a UL listed device (black box)?
Electric ranges are the same, smaller conductors but the insulation is rated for a higher temperature, in the past if nobody monkeyed with the wiring it was pretty much trouble free, now not so sure.
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,759
Location
Richmond, VA
But to the OP’s example/question, the 120V light bulb in the dryer is being fed from (likely) a 30A 240V breaker. How is this then safely done? Or do we just look away since the dryer is a UL listed device (black box)?
Guessing there is some OCP in the dryer
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,761
Location
NW Iowa
Inside of an appliance it's easy to determine what the load is. The light only pulls 1 amp so we can run small wire to it even though the whole appliance is on a 30.

Out in the world it's not so easy. There's no way to prevent someone from plugging in more than 15 or 20 amps on a 120 volt receptacle.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
When we run a 3 wire + ground conductor, I see that two hots are used for 240v needs and one hot/neutral is used for 120v needs as the bulb. This is how electric dryers are set up (afaik).

Can the same be done for multiple loads? For example, I was planning to run 30a circuit to gazebo for infrared heater. Can I add lights, fan and outlets on the hot/neutral for 120v? I realize I need to provide GFCI protection for 120v side but wanted to see if one circuit can suffice.

if it is a code violation, can you please explain why?

thanks
There are separate rules for tapping branch circuits and feeders. What you are talking about doing here is tapping a branch circuit, which falls under 210.19(A)(4) exception (1) covers what loads can be tapped . (c) covers what you are talking about. Individual outlets, other than receptacle outlets, with taps no longer than 18 inches are allowed. So no receptacles are not allowed since they are not listed in the exceptions.

As far as the dryer having 120 tapped off of 240, As long as that appliance is listed for that purpose, there is no violation. Starting with the 2017 NEC 422.6 All appliances operating at 50 volts or more shall be listed.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,050
Location
Modesto, CA
When we run a 3 wire + ground conductor, I see that two hots are used for 240v needs and one hot/neutral is used for 120v needs as the bulb. This is how electric dryers are set up (afaik).

The motor and controls in the electric dryer are also 120v...

Can the same be done for multiple loads? For example, I was planning to run 30a circuit to gazebo for infrared heater. Can I add lights, fan and outlets on the hot/neutral for 120v? I realize I need to provide GFCI protection for 120v side but wanted to see if one circuit can suffice.

if it is a code violation, can you please explain why?

thanks
no you cannot. your comparing internal wiring in an appliance that is listed by an NRTL and most likely has higher temperature rated wire and a load that is fixed and predictable (light and motor), to inside wiring in a building, feeding outlets, that would have no control over how much load is plugged into it up to 30a.... thats a recipe for a fire.... and a flawed comparison...
But to the OP’s example/question, the 120V light bulb in the dryer is being fed from (likely) a 30A 240V breaker. How is this then safely done? Or do we just look away since the dryer is a UL listed device (black box)?
A light bulb is a fixed load. Its not gonna pull more than its rated current. just like plugging in a 100w lamp, with an 18gauge cord, to a 15a or 20a circuit.... really the same concept...
 