240 heater

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
I just picked up a 5000 watts Hotzone radiant heater. The attached is the 240 hook-up (rated at 240/480). The installation manual suggests that this unit can be hooked up in "stages" or to a dimmer to control the output. How would I do that?
 

Attachments

  • 5000W WIRING TO 240V (1).pdf
    58 KB · Views: 38
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,316
Location
NJ
Without seeing a full schematic of the unit, it appears that there are 2 heating elements in parallel at the lower 240V configuration based upon the 1 pager supplied.

Easiest way to hook this unit up is to run both elements at once ( as per your pic) unless the unit is grossly over-sized.

Does this unit have an integral t-stat or require an external line-voltage or low-voltage t-stat?
 

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
:withstupi

That heater appears to have 2x 120V 2500W heating elements, with each element intended to use a different leg. Most 240V heaters don't use a neutral conductor.

I doubt the dimming or phasing is intended to be done internally.

You could use 2x 25A line level thermostats, 1 for each leg. Set 1 for 65* set the other for 60*. When temp drops below 65* the the heater puts out 2500W worth of heat energy, when the temp drops below 60* the other element comes on and the heater puts out the full 5000W.

If this is going into some sort of garage/workshop - I wouldn't bother with anything fancy.
 
To avoid these ads, REGISTER NOW!
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
It is going in a shop. Not sure how yet, but in a shop. If I use just one thermostat should it be a double pole?
 

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
It is going in a shop. Not sure how yet, but in a shop. If I use just one thermostat should it be a double pole?


You could get away with a single pole if the heater allows the elements to be run in series. If they must be parallel you'll need the double pole.
 