They're probably universal ballasts which will run on foreign Live and Neutral 240v not US Live and Live 220v.
Generally there is no 220v in the US, it is all 240v. The ballast could care less if its two opposing phase hots or a hot and an opposing phase neutral, it would not know the difference.
If you wire it for 240v you use a double pole light switch, it has four terminals on it and acts like two light switches in one. (these are NOT the same as a 3 way or 4 way switch) They are found as commercial and industrial, you won't find any spec or contractor grade. HD and Lowes has them, Leviton or Pass and Seymore brands. Of course you have to also use a double pole circuit breaker.
If you do this, I would take a marker or label-er and identify each fixture and box as 240v so if anyone else ever works on them, they understand. I know some 240 or 277v devices (photo cells for yard lights) will not function on a lower voltage once powered on a higher voltage. They actually burn out a resistor or something and would not work on the lower voltage after that, not sure if these ballast would work like that or not.
They do not wire any different, if you use romex, you need to take a red marker and color the ends of the white wire red at every termination so its apparent that the wire is not a neutral, only difference is that instead of running the neutral wire of a 120v circuit directly to the neutral bar in the circuit breaker panelboard, you instead run the wire to the "other" side of the double pole light switch and then from the switch to the "other" side of the double pole circuit breaker.
If this is in a residential building in the US (ie. attached garage) I seem to recall a NEC section that does not allow lighting circuits above 120v, but I haven't looked it up to confirm this.
Edit: I can find references in the code restricting the open circuit voltage of ballasted lighting used in residential to 300 or 1000 depending on the design, but cannot find any other restrictions, so my memory may be faulty.
Second Edit: NEC 210.6 may possibly limit the voltage but I'm not sure I understand it and would need mrb, Norcal, Aceman or another electrical guru on this board to tell me if I'm correct or not.
Charles