If it's a 30A circuit then ground needs to be #10. If circuit is 20A and you are upsizing to #10 then ground needs to be #10 too.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I remember a little match on ETF back in the day as to the reasoning behind it. Seems someone wrote about it at length but I cant recall the details.
 
OP
S

Shovelhead

Well-known member
Joined
Dec 22, 2018
Messages
397
Location
DEEP EAST TEXAS
Thanks fellers.
30A is the deal for the #10 grnd.
I couldn't remember if it was required or not.

No code where I'll be building but I operate like there is.
For most things anyway. LOL
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,219
Location
Modesto, CA
Code rules anyone?

youre in canada so the NEC doesnt apply. There is no point in commenting with canadian code for a US member...

But its 250.122(B)

Don't listen to them. If OP was in Canada with us, your answer is the correct one, but NEC has weird rules like the ground has to be the same size as the ungrounded conductors.

The OP is NOT in canada so your comment is moot.

Your comment in blue is not accurate.

The NEC doesnt require the grounding conductor to be the same size as the ungrounded conductor for ALL sizes of ungrounded conductors. only for #14, #12, and #10...
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Don't listen to them. If OP was in Canada with us, your answer is the correct one, but NEC has weird rules like the ground has to be the same size as the ungrounded conductors.

Canadian rules are the ones that are weird from our point of view. Also the comment that the ground has to be the same size as the ungrounded conductors is wrong. You need to stick to only citing Canadian rules.
 

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
716
Location
Southern Alberta
But its 250.122(B)


The NEC doesnt require the grounding conductor to be the same size as the ungrounded conductor for ALL sizes of ungrounded conductors. only for #14, #12, and #10...

Interesting. But that table doesn't reference the size of the phase conductor, it only references the "rating or setting of over current device".
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Interesting. But that table doesn't reference the size of the phase conductor, it only references the "rating or setting of over current device".

??? The table does give the conductor size of the ground. The amp rating also coralates to the ungrounded conductors. Not sure what you find interesting. The table gives the minimum ground size for circuit amperage.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,219
Location
Modesto, CA
Interesting. But that table doesn't reference the size of the phase conductor, it only references the "rating or setting of over current device".

Thats why you then reference table 310.15(B)(16), the core of the NEC.

You seem to be fishing for something but your net will come up empty...
 