Hello!

I am looking forward to buy a 240v 4000w heater which comes with a NEMA 6-20P cord.
My garage outlet is a NEMA 6-30P receptacle. I would rather not change the outlet.

Is there any risk using this kind of adapter cord? (this one from amazon)
1729705708997.png
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,732
Location
NW Iowa
I'd worry about the contacts in that crappy connector from Amazon. Weak contacts plus electric current cause heat. Don't want a fire.

It's why it's never recommended to use an extension cord with appliances like this.
 
Last edited:

BrandonV

Well-known member
Joined
Jun 9, 2023
Messages
4,030
Location
Arizona
Probably okay in actuality but I wouldn't do it. I'm not a fan of the factory cord and appliance being designed with an expected 20A OCPD not a 30A one.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,170
Location
SE MI
I'd worry about the contacts in that crappy connector from Amazon. Weak contacts plus electric current cause heat. Don't want a fire.
I had a heavy duty 18" long NEMA 5-15 3 way splitter. The 3 way end was molded in translucent plastic. After only a couple of years, you could see the arcing inside the plastic ! Cut that end off and replaced it with a 4x4 metal handy box with 2 duplex outlet. It might not be waterproof but it won't arc !
 
OP
N

Nathan3.0

Member
Joined
Feb 21, 2024
Messages
10
I will need to check my electrical circuit correctly, i have a fuzzy souvenir that my Dad did this cicuit for my air compressor which was 240V 20A breaker, and added this outlet (6-30R) to use a garage heater (NOT AT THE SAME TIME lol). But it was over 15 years ago...

If its correct, i could change the outlet to a 6-20r in order to use the right plug directly.

Here is a heater with 3750W which would make more sense. But over 200$ more expensive (yikes!)

 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,558
Location
Richmond, VA
I would also do the breaker and receptacle swap first. Second choice would be swapping the plug on the heater. I don't think I would go for the adapter
 
OP
N

Nathan3.0

Member
Joined
Feb 21, 2024
Messages
10
Well i took the time to check correctly during the weekend and here are my observations;

Panel breaker for this circuit is 20A
Wiring is 10/2 Gauge

I could probably replace the breaker for a 30A if the overall capacity is still ok, but this would require an electrician.
The "cheapest" (moneywise) would be be to get a heater with a 16A draw max and replace my outlet so i do not need to use a sketchy adaptor.

I thank you all for your imput :)
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,194
Location
The romantic hills of central Umbria, Italy,
I have made jump cords like that - always build them overrated for the highest current expected. If it's a 30 amp circuit, your wiring for your jump cord should handle at least that. Buying one premade -Reputable company (Schnieder, or the like), no prob. Unreliable company (People's Glorious Revolutionary Flower Pole Company of Electrical Guandong, Ltd.?) nope. Thats why I make my own. And I also check them occasionally to make sure they're in one piece, not getting warm, etc.

Your circuit is rated for 30 amps at 250 volts No problem with putting a 20 amp device on a 30 amp circuit, the only issue is if that device internally shorts, but if it does that you're likely going to have it try to pull more than 30 amps.

I'm also **** about wire sizing - if a circuit calls for #6, I'll up it to a #4, just because. (Other's, like Wylie and others on this here forum are more expert at electrical than I, If they say something take it to the bank, I only know what I personally would trust or not...) I refer to my Ugly's a lot to make sure I'm erring on the side of safety.
 