25 PSI on gas line test?

Ricardo99

New member
Joined
Sep 13, 2019
Messages
1
Location
Attached
My natural gas contractor extended my home gas line about 25 ft;
the city inspector wants a pressure test of 25 PSI for 15 min.

The gas contractor says that's not safe, that's too high of a pressure test and the shutoff valves themselves aren't rated for that high of a pressure test.

Is 25 PSI / 15 min pressure test legit?

Thanks for any info you can provide!

- Ricardo
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,329
Location
Richmond, VA
Have the city inspector provide documentation for the requirement then proceed. If it is memorialized in local code, then you will probably need to have the valves changed
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
If that is what the City inspector wants... As noted above, ask for a reference to double check just to be sure.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,839
Location
NJ
A 24 hour test with the piping filled to 15 psi is common in my area. You attach a 30psi full scale gauge on the system. Mark the starting pressure on the bexel and wait it out.
24 hours later, +/- 1 psi from starting pressure and your good to go.

Appliances need to be disconnected in case any valve were to leak, so you don't blow the appliance regulator.
 

1953mercury

Well-known member
Joined
Nov 25, 2012
Messages
701
Location
Steamboat Springs CO
I've done literally hundreds of these tests, and the pressure is really irrelevant. I use the same pipe and fittings on my shop air and it has handled 160# with no issues for over 30yrs. Give the inspector whatever he wants. Mike
 
To avoid these ads, REGISTER NOW!

Climatecreator

Well-known member
Joined
Dec 8, 2006
Messages
245
Location
CT
Gas pressures are usually only 1/2 a psi delivered to equipment or so. There's no need to test at super high pressure and no matter what pressure you're supposed to shut the gas ***** (the valve with handle by the appliance) so you don't damage the gas valve (the control that opens and closes to regulate the gas going into the appliance) if the delivery pressure is high to the house, sometimes 2psi etc a regulator will be placed on the line at the meter to lower it and this should NOT be there during the test.

Pressure test is ALWAYS determined by each individual inspector.

CC
 

alexb2000

Well-known member
Joined
Feb 7, 2010
Messages
664
Location
Fort Worth, TX
Guys I don't get the debate. Look up what the inspector is using as a code standard (on the city inspection website usually) then research the specific code.

For example the 2018 IFGC says under 406.4.1 the test pressure shall not be less than 1.5X max working pressure or less than 3 psig. Test pressure when it exceeds 125psig it cannot exceed 50% of the pipe rating.

25psig seems completely reasonable.

Duration of testing 406.4.2 says that testing for a single family residential unit shall not be less than 10 minutes or exceed 24 hours.

15 minutes is also well within this code.

I would find another gas contractor, perhaps one that can read.
 

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
Do what he requested. As stated appliances must be disconnected and line side capped or plugged .
By me , local natural gas supplier will stop by and witness test pressure. Then return next day to verify pressure.


Sent from my iPhone using Tapatalk
 