Hello

I've seen this before in the old house and I'm seeing it again in the new one. On circuits that have been shut off at the breaker, I can read 26 to 36 VAC across the black wire and neutrals or earth ground. Anybody have input?

Thanks Stewart
 
To avoid these ads, REGISTER NOW!

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
Yes, digital voltmeters can read bleed-over from adjacent wires. There is hardly any current available at this ~30 volt level. Even the impedance of a cheap analog volt meter will pull the voltage down to nothing.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Phatom voltage is not exactly the right description....

What you are seeing is 'induced' voltage. This is a good example of what happens when wires pass parallel to each other over a distance.....I have seen as much as 80-90 Vac....

The good news is that it's a low current....if you grab the wires, in most cases there is not enough current for you to feel anything.
 
To avoid these ads, REGISTER NOW!

TurnipTruck

Well-known member
Joined
Aug 28, 2005
Messages
1,590
Location
Southcentral Alaska
I see this at the plant all the time. I recently had a problem at work where a 120Vac relay was intermittently energized by induced current when a strobing DC signal RUN IN THE SAME 1000' CABLE AS THE AC POWER caused mystery shutdowns. I measured 80+ Vac with the far end of the AC wires disconnected.
 

LoneGunman

Well-known member
Joined
Mar 27, 2007
Messages
2,081
Location
The Gunshine state
That's why I still use an old school "wiggy" (solenoid operated tester) as my main tester, no reason to break the expensive Fluke out for 99% of jobs and the "Wiggy" won't read low current voltages because the solenoid is using the current.
 