28x52 heater sizing

Soccer918843

Well-known member
Joined
Aug 16, 2020
Messages
52
Location
Upstate ny
I have a 28x52x10’ walls I’m gonna put a corner propane unit in. But not sure on the btus. I have two insulated garage doors on the front 8x9 and one on the back 7x9 I have 3 insulated windows and two insulated man doors. R23 mineral wool in the walls and r30 mineral wool in the ceiling with the upstairs of it being uninsulated and not heated . Thanks
 
To avoid these ads, REGISTER NOW!

Racy2

Active member
Joined
Feb 24, 2019
Messages
39
Location
Bolton, Ontario
I have the same dimensions as you with the exception of 12 foot walls. I went with a 80,000 BTU hanging gas heater and 2 fans. Has not been cold enough yet to experience any heat. I was informed by the builder that this setup would be very good. I plan on heating the garage all winter. Our temperature here will be a few degrees colder on average.
 

Will S.

Well-known member
Joined
Apr 15, 2010
Messages
446
Location
The First State
36x48 with 12' walls to 16' ceiling. 85kbtu Reznor LP, a bit over-sized, but I got a smokin deal on a dealer's showroom display model that was never installed. Been in for 10 years. Love it.
 
OP
S

Soccer918843

Well-known member
Joined
Aug 16, 2020
Messages
52
Location
Upstate ny
Thanks I’m Looking at the Sterling 2 stage one and there recommending me a 105k btu model for my size and I thought that might be a little over kill... they make a 75k and a 90k as well
 
To avoid these ads, REGISTER NOW!

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
36x48 with 12' walls to 16' ceiling. 85kbtu Reznor LP, a bit over-sized, but I got a smokin deal on a dealer's showroom display model that was never installed. Been in for 10 years. Love it.

I have an out-building the same sf -- It's two connected buildings open to each other -- even higher ceiling on one side.

Well insulated -- the propane unit nets out around 32k BTU. It's in PA and has no trouble keeping the space 70.
 

toyotadriver

Well-known member
Joined
Dec 30, 2010
Messages
1,586
If you heat it all the time you don’t want to oversize it. If you will only heat when working in there then I’d recommend sizing it on the larger side. I heat a 30x40x10 shop with an 80k. Well insulated but I only heat it when it gets used. Lowest temp it ever gets inside without heat is about 40* but usually stays between 45*-50* without heat. That said, I like to work out there with the temp around 62*-66* so it needs a fair amount of BTUs to warm up the air as well as the cold soaked tools and equipment.
 