I needed about 35' of 3 conductors with ground to go between two three-way switches. I had some empty 3/8" MC and solid 12-gauge THHN in black, red, white and green so I filled the MC with the four conductors and roughed in the assembled wire and MC. ...I would swear I saw 12/3-3/8" MC at my local big box hardware store. For some reason I decided I better check to see if that fill was allowable and now am confused and concerned. Which information is correct?
Southwire Conduit Fill Calculator = 38.41% fill (yes, fill is okay to use)
Or my books?
12 gauge THHN = .0133 sq/in each
.0133 * 4 = .0532 sq/in
3/8" MC at 40% fill = .046 sq/in maximum fill (no, fill greater than allowable capacity)
Southwire Conduit Fill Calculator = 38.41% fill (yes, fill is okay to use)