3 HP compressor motor-single phase

qmdv

Well-known member
Joined
Dec 20, 2012
Messages
54
I have a really good air compressor that has a 3 phase 3 HP motor that turns 1800 RPM. We are moving and will no longer have three phase. I have been looking for a replacement motor and have noticed that most of them are 3450 RPM. Wonder why that is the case. !750 RPM are available but not near as many as the higher
 
To avoid these ads, REGISTER NOW!

strutaeng

Well-known member
Joined
Dec 12, 2011
Messages
2,244
Location
Dallas, TX
I've seen more 5HP than 3HP for sale in the used market. Most are 1725 RPM in both of those HP ratings.

If you happen to find a 5 HP instead, you can install that also without changing anything else. Motor would just draw less amps, comparable to the 3 HP.

I've got an air compressor with a Curtis pump 7.5-10 HP. Motor is 10HP, but reduced with pulley so that it is runs as a 7.5 HP.

Even that is way too much for things like DIY pneumatics. I only fire it up when using HVLP air hog.

Anyway, point is that a larger HP would also work if it is cheaper to buy.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,693
Location
NW Iowa
Just match the frame size, hp and RPM. Then it will bolt on with no other changes.

Guessing you are finding 3450 motor because you are searching for "air compressor motor". The cheap compressors often use them. It's just a motor, match the stuff above and you will be fine.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I have a 3 and a 5. The 3 is the master and don't even have the breaker on to the 5, its demand/backup and I so rarely need it no reason to leave the power on. I got 200 gallons of tanks, air on 24/7. Leaves me with longer run times with a bit smaller motor, easier starts on rural lines. 4 minute recharge cycle.
3 of old were mechanic compressors, air tools, pumping tires including hi pressure truck tires. 5 became more popular with 100A service and body work. The price narrowed, standards and expectations went up, 5 has become the benchmark.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
2 stage, 5 hp 80 gallon tank can do most work a man can do, recharges fast, will outfit several mechanics, will do the body work for one man continuous. 2 men can share in a small shop, have seen a lot done on a 5. Normally doing a calc, 7.5 for 2 and 10 hp can do 3 or 4 pretty easy not counting 100% cap sandblast.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I did a setup on a truck shop. It was a bit of a challenge come to air to reason with the new owner that it was great we had 25 hp comp we didn't need to pipe everywhere 1.5 inch. Didn't need to go everywhere the same circuit on huge pipe.
 

strutaeng

Well-known member
Joined
Dec 12, 2011
Messages
2,244
Location
Dallas, TX

Amp draw is a function of work done. So if the pump, rpm, pulley are kept the same, the CFM produced will be the same for both motors, i.e, the "work done" is same.

Say the 3HP is drawing "X" amps. The 5HP will draw similar amps. There's torque curves, efficiency, etc., but in round numbers both will be similar.

The 5HP is not working at full capacity, therefore not drawing full amps.

The air compressor I mentioned has continuous-run mode. When the tank gets full, the pilot valve sends air to the the pump head and the compressor "free-wheels." I've checked with ammeter and it's drawing like 1A because it's not pumping air.

I'm not an electrician, just stating the basic physical theory.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
The 5HP is not working at full capacity, therefore not drawing full amps.

Maybe slightly less amps, but not simply 3HP's worth of amps.

The lighter loaded 5HP motor will have a worse power factor. (i.e. 'wasted' amps). The circuit would still need to be sized for the 5HP motor's FLA.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Maybe slightly less amps, but not simply 3HP's worth of amps.

The lighter loaded 5HP motor will have a worse power factor. (i.e. 'wasted' amps). The circuit would still need to be sized for the 5HP motor's FLA.

In the US, the circuit wire needs to be sized by table 430.248 and the motor HP. for 5HP this means 28a and #10 THWN or #8 NM-b
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,904
Location
Coronado, CA
Quote:
Originally Posted by u2slow View Post
Maybe slightly less amps, but not simply 3HP's worth of amps.

The lighter loaded 5HP motor will have a worse power factor. (i.e. 'wasted' amps). The circuit would still need to be sized for the 5HP motor's FLA.

In the US, the circuit wire needs to be sized by table 430.248 and the motor HP. for 5HP this means 28a and #10 THWN or #8 NM-b

If your compressor use is minimal and your power is cheap (like Solar) maybe the waste due to power factor will be of little or no consequence.
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,693
Location
NW Iowa
Quote:
Originally Posted by u2slow View Post
Maybe slightly less amps, but not simply 3HP's worth of amps.

The lighter loaded 5HP motor will have a worse power factor. (i.e. 'wasted' amps). The circuit would still need to be sized for the 5HP motor's FLA.



If your compressor use is minimal and your power is cheap (like Solar) maybe the waste due to power factor will be of little or no consequence.

Good thing power isn't billed by amps. We pay for watts which is the real power used.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
Power factor doesn't have a billing consequence (in residential, typically), but the circuit is still subject to a higher current, and that may require larger wire; despite only pulling 3HP out of the 5HP motor.

In the US, the circuit wire needs to be sized by table 430.248 and the motor HP. for 5HP this means 28a and #10 THWN or #8 NM-b

Neato. In Canada we size by motor FLA. When the equipment isn't there, then we use the HP table. :thumbup:
 
To avoid these ads, REGISTER NOW!

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
VFD definitely has to be oversized for compressor use.

It's only viable vs a single phase motor if you buy a super cheap VFD. I've been down this rabbit hole and concluded the single phase motor makes the most sense. I also don't have to worry that it's been set up correctly and wait to see if either the motor or VFD let their smoke out on initial power up.

A 3hp, single phase motor is not hard to find.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
I also don't have to worry that it's been set up correctly and wait to see if either the motor or VFD let their smoke out on initial power up.
Only 5 wires+a ground are requires to hook up a VFD.
A 3Ø disconnect takes 6+a ground.
Do you worry when someone first powers up a disconnect?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I used to fool with every gadget they made and in the end cost more and sometimes never really got done or done right. If I could and the start would work would be looking for a single phase, could even plug it in at 3 hp.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
Only 5 wires+a ground are requires to hook up a VFD.
A 3Ø disconnect takes 6+a ground.
Do you worry when someone first powers up a disconnect?

It's not the number of wires, it's making sure they are on the correct terminals that I would be concerned with. Especially with instructions written in Chinglesh and the fact that none of these VFDs have standardized terminals or labeling. There's also the options of making sure that reverse is locked out, soft start, etc. There's a bit more going on than just connecting five wires + ground.

A three phase disconnect isn't relevant if you are swapping to a single phase motor.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
All the drives I've hooked up were clearly labeled L1, L2, (and where used) L3 for the line side and T1,T2,and T3 for the load side.
They come with a basic default program setting, which is enough for a compressor that doesn't need bells and whistles like computer inputs.
Low quality no name ChiCom drives tend to have manuals that are written with the help of a Chinese to English dictionary. The better quality drives have their manuals written in grammatically correct English.:)
 

FTG-05

Well-known member
Joined
Oct 11, 2012
Messages
1,517
Location
TN
All the drives I've hooked up were clearly labeled L1, L2, (and where used) L3 for the line side and T1,T2,and T3 for the load side.
They come with a basic default program setting, which is enough for a compressor that doesn't need bells and whistles like computer inputs.
Low quality no name ChiCom drives tend to have manuals that are written with the help of a Chinese to English dictionary. The better quality drives have their manuals written in grammatically correct English.:)

If I can wire a 3 phase motor to a one phase 230 vac VFD (KBAC-27D), then anybody can. It's pretty simple, even I could figure it out.

2x72 belt grinder with a Weg 2hp motor. Not saying that's the way to go for a compressor. But for a 2x72 belt grinder, it's the shiznit.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
Since the sub-point about wiring (taken out of context) seems to have a life of its own, my main point was you can get a quality 3hp, single phase motor for less money than a cheapie (read questionable life), appropriately sized VFD.

I'd be all for a VFD if we were talking about a use that variable speed were beneficial.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Since the sub-point about wiring (taken out of context) seems to have a life of its own, my main point was you can get a quality 3hp, single phase motor for less money than a cheapie (read questionable life), appropriately sized VFD.
I'd be all for a VFD if we were talking about a use that variable speed were beneficial.

How could it be taken out of context when the first 3 letters in your first post of the thread were "VFD"?
More like just the natural progression of the thread
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
It's out of context because you turned correct wiring into the reason for or against using a VFD. The main reason I stated no on using a VFD is cost. Getting the wiring done correctly wasn't the driver, it was a hitchhiker that happened to be riding along.
 
Last edited:

marinusdees

Well-known member
Joined
Oct 30, 2012
Messages
1,325
Location
Edgewood, Washington
All the drives I've hooked up were clearly labeled L1, L2, (and where used) L3 for the line side and T1,T2,and T3 for the load side.
They come with a basic default program setting, which is enough for a compressor that doesn't need bells and whistles like computer inputs.
Low quality no name ChiCom drives tend to have manuals that are written with the help of a Chinese to English dictionary. The better quality drives have their manuals written in grammatically correct English.:)

"Grammatically correct" does not translate as "intelligible"..At least not to an old fart like me.
 

marinusdees

Well-known member
Joined
Oct 30, 2012
Messages
1,325
Location
Edgewood, Washington
I said it in response to the "Chinglesh comment"
The manual's written in plain English
Judge for yourself:) https://www.vfds.com/manuals/hitachi-sj200-manual.pdf

Holy s---. I haven't got time to read nor can I understand all this stuff. Even if I was an EE, given the era I'm from I don't need all this . And, I have 9 years of education beyond High School. Guess I wasted my money or have a pea-sized brain, you choose. And, I have four VFDs in my shop. Makes me a kind of a genius, maybe.
You are obviously several intelligence levels above me. I'm totally in awe.
 
Last edited:

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
So in my first post which started this back and forth I specifically said super cheap VFDs would be the only way to financially make it viable to use a VFD. You equate that to mean Hitachi?

Again, more context loss.:dunno:
The better quality drives have their manuals written in grammatically correct English.:)
No :lol_hitti
That was an example of one of the better drive manuals, not the Chi-com cheapo written in as you say "Chinglesh"
 
Last edited:

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
You asked a question. I answered it and it's somehow irrelevant?
I think you may have a problem with reading comprehension.

Do I? The relevant context is cheapo VFDs for their price of entry vs a new motor and the manuals that accompany them. We all know that there are better VFDs out there. We all know that these better VFDs likely come with better documentation. WE also know that there's a cost associated with that which makes them not such a good option for the OP's situation. You may as well have just suggested the OP get a new compressor. It would have had as much value.

Call it reading comprehension if that means you can't go beyond the latest reply in mind at any given time. I'll call it staying on topic.
 