Mustang51js
Well-known member
Ok,I want to run this by some of the guys on here that work with 3 phase stuff and havc more often. It's a rare thing for me so any help would be great. I have two havc units to hook up. Paper I have from guy says mca-65.5 amps, mocp-80 amps. Fla-69 ,lra-365. It's 208/230 3 phase. The model number is 50tc d14 if anyone is familiar with them. So this is what I came up with,my plan is to run one pipe since they are in line with each other along the roof. I was planning on 1 1/2 emt up wall and over about 30 feet to a 12x12 j-box by first unit then continue on about 30 feet to next unit. I would run 1 inch nonmetallic flex up to each unit. I am thinking about using #4 thhn and #8 ground. So I would have 6 #4 thhn,1 #8 green thhn ground,and #12 thhn black and white for gfi and light on each unit. I figure #4 is rated for 95 amps,70% derated for pipe fill I'm looking at 66.5 amps. If I decide to run a mc wire along side instead of in the pipe I can derate at 80% which would be 76 amps. I think I'm good with the first option with everything in same pipe but want to see what you guys think. Will be on a 80 amp breaker. Am I ok with using the 90degree rating and calculations.total run from panel to last unit is about 100 feet.