3 phase compressor trips overload

Eli D

Active member
Joined
Sep 26, 2020
Messages
30
Location
Oregon
I have my dads old compressor and lately it has been kicking off at the overload. I don’t know a lot about electrical diagnosis. If I reset it the compressor runs fine for a while it has a 5hp motor. Thanks for any help
 

Attachments

  • FF8F866C-60BF-4277-B6AC-A8E8E4813990.jpeg
    FF8F866C-60BF-4277-B6AC-A8E8E4813990.jpeg
    675 KB · Views: 41
  • 47E25C49-F37A-4297-9CAF-587F0903E563.jpeg
    47E25C49-F37A-4297-9CAF-587F0903E563.jpeg
    715 KB · Views: 41
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,847
Location
NJ
Is it tripping at re-start or while building pressure?

What's the actual voltage while running?
Put an ammeter on it.
What size overloads are in it?

If you remove the belt does it still trip? What is the current w/o belt?
 
OP
E

Eli D

Active member
Joined
Sep 26, 2020
Messages
30
Location
Oregon
Is it tripping at re-start or while building pressure?

What's the actual voltage while running?
Put an ammeter on it.
What size overloads are in it?

If you remove the belt does it still trip? What is the current w/o belt?
It trips intermittently, so far I haven’t noticed when other than when my tools quit working. Today it worked fine all day and didn’t trip. I will check voltages tomorrow.
in addition to the above, what voltage is the motor wired for? its a dual volt motor...
220 v

Thanks for the help.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
It trips intermittently, so far I haven’t noticed when other than when my tools quit working. Today it worked fine all day and didn’t trip. I will check voltages tomorrow.

220 v
It clearly says 230/460 on the nameplate.
It's either a 208V(Wye) or a 240V(Delta) supply voltage. 230V is made for a 240 supply only.
If it were 208V it would be marked 200/230 (200V motors are made for a 208V system).
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,847
Location
NJ
It trips intermittently, so far I haven’t noticed when other than when my tools quit working. Today it worked fine all day and didn’t trip. I will check voltages tomorrow.
Do you have an ammeter/clamp-on?

Also after removing the belt, see how the motor spins. Any noise? gritty feel?

Do the temps climb around the output shaft after in runs for a while?
 
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,307
Location
Dutzow Missouri
Just to be clear are you saying the 50-amp breaker in the photo is tripping and the only load is the 14-amp motor?

Seems like if it was a motor problem the overload on the motor would trip long before a correctly sized breaker.

Is it possible someone install a replacement motor on this compressor without the required motor overload?

It also seems very likely that if enough power to trip a 50 amp breaker passed thru your motor the motor would have smoke pouring out of it and would never run again.

How sure are you that the screws holding the wires to the breaker are tight?

Walta
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,847
Location
NJ
Just to be clear are you saying the 50-amp breaker in the photo is tripping and the only load is the 14-amp motor?

Seems like if it was a motor problem the overload on the motor would trip long before a correctly sized breaker.

Is it possible someone install a replacement motor on this compressor without the required motor overload?

It also seems very likely that if enough power to trip a 50 amp breaker passed thru your motor the motor would have smoke pouring out of it and would never run again.

How sure are you that the screws holding the wires to the breaker are tight?

Walta
There is no 50a cb. That is a definite purpose contactor above an o/l relay.

As best I can read the FLAs are 14.4A @ 230V.

The heaters are N42's. The N42's are supposedly rated for ~26.5 - 37.5a........way oversized.

You need to find out the overload relay part number. Then you'll know which table to use in this A-B heater chart.

https://rockwellautomation.custhelp.com/ci/okcsFattach/get/18673_4 Best I can guess you should have N35-N37's
 
Last edited:

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,075
Location
AZ
Inspect the contacts and see if they’re burned and pitted. There is a specific voltage drop test that can be performed but not something I’d suggest you perform.
 