I have. 7.5hp three phase compressor. Looking to buy a digital phase converter. When I buy, do I buy a 7.5 digital phase converter or do I have to go to 15?
 
To avoid these ads, REGISTER NOW!

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,529
Location
Hutchinson Ks.
I think Phase Perfect is what you are talking about? Kinda like an inverter actually IS an inverter with more logic. I think the 10HP is the one you want, hard starting equipment like a compressor I would ask the company about first.
 

jar944

Well-known member
Joined
Jul 26, 2010
Messages
6,011
Location
Northern VA
I have got to think retrofitting a single phase 7.5hp motor is much cheaper
than buying a 10hp Phase Perfect unit, even used.

-D

Sure but then you can't freely add a bunch more 3ph machines.

Imho a for a single application a vfd is the cheapest option.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,478
Location
SE MI
I think Phase Perfect is what you are talking about? Kinda like an inverter actually IS an inverter with more logic.
To the best of my knowledge, ALL electronic phase converter, certainly any that have variable frequency/speed control, convert the single phase AC to DC and then take the DC and convert it to 3 phase AC.

Somewhere in there, they may or may not boost/reduce the incoming voltage to create the proper output voltage. Because the 3 phases are "synthesized", there is feedback circuitry to ensure the proper voltage and phase angle of L1, L2 and L3.
 

jar944

Well-known member
Joined
Jul 26, 2010
Messages
6,011
Location
Northern VA
I see DPS online they are around 400
Thats a static phase converter. You only get 2/3 the rated hp from the motor since its only running on 2 of the 3 phases. You want a varible frequency drive.

This one will provide 27FLA off single phase power.
Screenshot_20240411_091352_Chrome.jpg
 
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,014
Location
Peace Valley,mo
Compressor have a working unloader? Go by name plate amps double it might want to go up to 20 hp vfd if it needs service factor amps.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,316
Location
Dutzow Missouri
The black boxes labeled “digital phase converter” are mostly 1930 technology of a static phase converter with a digital timer to disconnect one of windings after the motor is turning. Note this static converter is poorly for heavily loaded motors of an air compressor and very likely to destroy your motor.

If this is likely to be the only 3 phase machine you are going to acquire (fat chance) get a VFD that will produce real 3 phase power. If you are likely to get a few more 3 phase machines get a rotary phase converter.





Walta
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,478
Location
SE MI
I would think that ALL modern digital phase converters would have built in "soft start" capability. With a true soft start, LRA should not be an issue.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,316
Location
Dutzow Missouri
Do not be fooled by the word digital.

The low cost devices are a few capacitors a relay and a digital timer.

That do not feed current to all the phase evenly and will damage motors under heavy loads.

The phase perfect looks like a good product but at that price point you can get a VFD.



Walta
 

cycle61

Well-known member
Joined
Apr 5, 2020
Messages
500
Location
Middle of Oregon
Do not be fooled by the word digital.

The low cost devices are a few capacitors a relay and a digital timer.

That do not feed current to all the phase evenly and will damage motors under heavy loads.

The phase perfect looks like a good product but at that price point you can get a VFD.



Walta

The phase perfect is a very good product, it uses the two incoming lines and then pulls off a bit of power, feeds a DC bus, and generates a true third leg with an inverter circuit.

If you need variable speed, get a VFD. If you need to power a 3/ machine on a single phase service and might ever consider adding another machine, go for a phase perfect.
 

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,529
Location
Hutchinson Ks.
As mentioned above, for a single use like the compressor. A single phase motor may be the most cost effective and correct choice. Machine tools particularly CNC with regenerative braking need three phase power from mains or something like Phase Perfect.

Rotary phase converters can work on many machines but the issue with leg balance and hard starts require oversizing for a machine like a compressor. Static converters are just start modes to single phase a three phase motor. An inverter VFD would also be a good choice BUT, the cost of the drive may exceed a replacement motor? A 7.5 HP 1750 single phase motor is about 800.00. How much is a single phase input VFD?
 

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,529
Location
Hutchinson Ks.
$795.20 plus tax and shipping, but you don't have to buy a new starter to make it work like with a single phase motor.
Depends on the starter? I have a number of inverters, they are all 480 three phase, the low cost single phase VFD's seem to be hit or miss? I have no experience with them, just what I read on various forums?
 

jar944

Well-known member
Joined
Jul 26, 2010
Messages
6,011
Location
Northern VA
Depends on the starter? I have a number of inverters, they are all 480 three phase, the low cost single phase VFD's seem to be hit or miss? I have no experience with them, just what I read on various forums?

7.5hp 3ph should be a nema size 1 starter, 7.5hp 1ph would be a size 2.
 
To avoid these ads, REGISTER NOW!
Top Bottom