You can use a dryer plug and receptacle that has a separate neutral and ground. Use the ground as ground and the neutral as one of the 3 power legs.
You can use a dryer plug and receptacle that has a separate neutral and ground. Use the ground as ground and the neutral as one of the 3 power legs.
You can use a dryer plug and receptacle that has a separate neutral and ground. Use the ground as ground and the neutral as one of the 3 power legs.
The only safe and correct answer is to use a proper three phase connector which will have five pins: ground, neutral and three phases.

Just exactly where does the "neutral" come into the picture??![]()
Just exactly where does the "neutral" come into the picture??![]()
120/208 wye has three phases, and a neutral. Whether he uses it or not is not the issue, it exists and needs to be on the plug.
There are two ways to do things, the right and proper way and kludged with the eventual probability that the kludge will come an bite one some day.
120/208 wye has three phases, and a neutral. Whether he uses it or not is not the issue, it exists and needs to be on the plug.
There are two ways to do things, the right and proper way and kludged with the eventual probability that the kludge will come an bite one some day.
120/208 wye has three phases, and a neutral. Whether he uses it or not is not the issue, it exists and needs to be on the plug.
There are two ways to do things, the right and proper way and kludged with the eventual probability that the kludge will come an bite one some day.
you dont have to use a connector with a neutral unless your load requires one. L15 connectors are installed in 120Y208 systems all the time for 3P4W loads
To clarify, your response makes reference to "3P4W Loads" which by definition indicates a system configuration of 3Phase, 4Wire therefore requiring a neutral.
When referencing a receptacle, the correct and complete identifier is "3P4W Grounding" which indicates 3Pole 4Wire of which one of the connections is reserved for a ground conductor and hence does not include a neutral.
Key differance is Pole versus Phase and load requirements (system configuration) versus receptacle NEMA configuration.
JP
there has always been confusion using this reference between 3 phase systems and connector configuations. In connectors, 3P4W is 3 poles and a ground. Can be either 3 hots, or 2 hots and a neutral. Something non grounded would have equal numbers, for example I have a nema 18-60 plug (common in older hotel ballrooms) which is non grounding. This is referred to as 4P4W -has 3 hots and a neutral, no ground. Back to 3P4W, whether its 3 phase or not is determined from the voltage rating ex: 125/250 or 3 phase 250.
Yes, it can be confusing and that was the purpose of my post as you were referring to "Loads" instead of the receptacle (or connector as you note).
Your example of the NEMA 18-60 receptacle is correct as a 4P4W but only if you add the clarification of "NON GROUNDING" at the end so as to reference the receptacle configuration and not the system configuration. The reference to receptacles for #Poles #Wires should always follow with GROUNDING or NON GROUNDING.
Voltage rating has nothing to do with the system configuration notations. You can have 1P3W (single phase 3 wire) or 3P3W (three phase three wire) or 3P4W (three phase 4 wire) all of which can be a multitude of voltages. For example I can have a 3P4W system configuration that would be valid for 120/208V or 277/480V or 7200/12470V.
JP
NOTE Phase converters are all delta wound so how do you get wye power as you assume.
also the idea of re purposing stuff that has the potential to cause great bodily harm is plain *** stupid
Back to your original question. Why wouldn't you just hard wire both machines to the converter? What are the machines? Usually, once one machine is running the other machine can be started. The first machine acts as a rotary converter for the second.
Then why bother with plugs and receptacles?