Hey all, just picked up a three phase air compressor. My question is, I have 100amp breaker box of single stage power to the shop. The motor requires a 30 amp breaker at 220v to push the 5hp motor. The required line is 10AWG or 14THW. If I hook up the motor to a 50AMP breaker would this melt my panel? I know with 3 phase that it's off loading the power down l1,l2,l3 on a breaker box. This is just to get the motor to rub properly. The motor is a Baulder motor and I don't want to melt it.

What do you all suggest? It does have a 3 phase magnetic starter on it. Which I would assume I'm going to need a single phase magnetic starter? At a lost on what I can do unless I spend large money to actually drop three phase there.
 
To avoid these ads, REGISTER NOW!
OP
B

bannerd

Well-known member
Joined
Nov 14, 2011
Messages
209
Location
Upstate NY
I was looking at a rotary box as well, but I'm not sure if these are going to be replaced every year. Capacitors seems to go on them in doing some research.
 

bsg

Well-known member
Joined
Feb 10, 2009
Messages
330
Location
Imlay City, MI
Why would you try and run a 30 amp load on a 50 amp breaker?

You need three phase power to start that compressor, no way around it without buying a new motor and controls to change it to single phase.

I don't know where you got your info on the converter, some of them run for years without any problems.

Do you plan on buying any other three phase equipment, mill or lathe?

If you do, what I would do is put in a three phase panel fed from a rotary converter.
There are lots of options here and you will need to plan out what would be the best solution for you.

Three phase power in the shop is not that hard to do but you have to plan ahead.

You first have to ask yourself, is this the only piece of machinery that will require three phase?

Kevin
 
Last edited:

MixManSC

Well-known member
Joined
Jan 6, 2014
Messages
154
Location
South Carolina
Yep.... there is really no viable way to run that motor on single phase power. You either need a phase converter or change out the motor on the compressor to a single phase motor. If you want a Baldor single phase 5HP motor you are looking at $350 to $450 - or you could go with another brand motor and probably get that cost down to $200(ish). Even lower if you can find a used motor. Just needs to be the same speed, mounting, shaft size, and duty cycle.
 

Strouty

Well-known member
Joined
Mar 21, 2010
Messages
38,244
Location
Southern Maine
An air compressor is the worst choice for a converter. Just change the motor. I will be interested to see if we are missing something from the OP or if he just doesn't understand.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,238
Location
Modesto, CA
Hey all, just picked up a three phase air compressor. My question is, I have 100amp breaker box of single stage power to the shop. The motor requires a 30 amp breaker at 220v to push the 5hp motor. The required line is 10AWG or 14THW. If I hook up the motor to a 50AMP breaker would this melt my panel? I know with 3 phase that it's off loading the power down l1,l2,l3 on a breaker box. This is just to get the motor to rub properly. The motor is a Baulder motor and I don't want to melt it.

What do you all suggest? It does have a 3 phase magnetic starter on it. Which I would assume I'm going to need a single phase magnetic starter? At a lost on what I can do unless I spend large money to actually drop three phase there.

The only way to run a 3-phase motor on single phase power is to use a converter. Changing the breaker will do nothing. No u wont burn up your panel but instead burn up the motor because its single phasing which will cause it to overheat!

I would build an RPC!

For wire u need either #14 THHN or #12 NM-B. #10 is overkill. 30a breaker should be fine!
 
Last edited:

Bib Overalls

Well-known member
Joined
Dec 4, 2006
Messages
3,318
Location
Jonesboro, Arkansas
A simple static phase converter will cut your hp by 1/3 and that will certainly affect your compressor's efficiency. What you need is a rotary phase converter with an idler motor of at least 7.5 hp and 10 hp would be better. I have had good luck with rotary phase control panels made by Phase-Craft and sold on eBay. Talk to Jim at Phase Craft. He is a good guy and honest with his recommendations.
 
Last edited:
OP
B

bannerd

Well-known member
Joined
Nov 14, 2011
Messages
209
Location
Upstate NY
Looks like I need to run a rotary phase converter. The motor on there now is about $2,000 and is a baulder motor. The Maximum amps it requires is 30AMP so I will need to pick one of those up. I can't run a single phase motor on this unit, the magnetic starter is all three phase. To replace that I would be spending a lot of money. The air compressor was a really good but, picked it up for $200.

Also, this will be the only piece of machinery that will require three phase. I don't think down the road we will ever get into machinery.

http://www.ebay.com/itm/5-HP-ROTARY...607?pt=LH_DefaultDomain_0&hash=item45fa633b0f

Bib Overalls: Those looks like really good buys, thanks!
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
No matter how cheap it is the thing is scrap unless you have the power to run it, this is not for you. Buy a new motor or sell it to someone that can use it.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
A rotary phase converter or single phase to 3-phase VFD will cost more than a new 240Vac single phase motor.

Then you sell the 3-phase motor on Ebay and get half your money back.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
This is where internet advice gets skewed. All that equipment is for a different user unless he wants to admitedly fart and fiddle. The motor on there might be 2 grand new in some cases but not in the used market. There is a glut and shortage of single phase.
Its why that gem was 200$, if the pump is a treasure and it has a good tank its worth a new quality motor. I have a 3ph controller on one of my old units, someone give it to me.

I live on rural power, nearest 3 is 2 miles, wish it would come by with new poles etc. I do have 400A service but part of it is I can and didn't cost me anything when I did service upgrade. There are some guys that can, I can, my neighbor can do without another layer of equipment above 50A, one has a converter and 1 planer, the whole setup is a space hog, just a bunch of extra stuff. He can and had free parts.

I wanted to stay in a world I didn't have to modify service every time I shifted something around or wanted to use elsewhere.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I use 2 comps, a 3 and a 5. Its all hooked together so I got about 200 gallon on, reduces cycles. But the high dollar 3 hp is nicer to the service. I just ran the other one a couple cycles while I was putting new brgs in the 3,,, could tell when the 5 came on.
 
To avoid these ads, REGISTER NOW!
OP
B

bannerd

Well-known member
Joined
Nov 14, 2011
Messages
209
Location
Upstate NY
Thanks for the ideas, I went out to the shop and looked over the compressor again. It looks like the huge magnetic starter on there can be converted to single phase using the L1, and L2. I'm going to try and source a single phase 220v motor, be the easiest route.

The closest three phase power to use is ten miles, which would cost way to much to actually get installed. If we decided to get more three phase equipment we will have to look into converters.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
The 3 phase starter can be used on a single phase system, it's done all the time in industrial applications. You just have to run one of the legs thru 2 of the starter contacts (load side of B phase to line side of C phase, connect motor to A and C phase)
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,927
Location
oregon
Looks like I need to run a rotary phase converter. The motor on there now is about $2,000 and is a baulder motor. The Maximum amps it requires is 30AMP so I will need to pick one of those up. I can't run a single phase motor on this unit, the magnetic starter is all three phase. To replace that I would be spending a lot of money. The air compressor was a really good but, picked it up for $200.

Also, this will be the only piece of machinery that will require three phase. I don't think down the road we will ever get into machinery.

http://www.ebay.com/itm/5-HP-ROTARY...607?pt=LH_DefaultDomain_0&hash=item45fa633b0f

Bib Overalls: Those looks like really good buys, thanks!

I would really like to see pictures of this set-up. Include the nameplate on the motor please. With this information we can give you a lot better detailed advise. Realize that the unit linked to on e-bay will also require you to purchase an additional 3 phase motor for the 'rotary' part of the converter. What is being sold is only part of a rotary converter setup.

lg
no neat sig line

lg
no neat sig line
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,238
Location
Modesto, CA
The 3 phase starter can be used on a single phase system, it's done all the time in industrial applications. You just have to run one of the legs thru 2 of the starter contacts (load side of B phase to line side of C phase, connect motor to A and C phase)

Why do u have to do that? I have seen 3-phase starters used with only 2 contacts connected...
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Why do u have to do that? I have seen 3-phase starters used with only 2 contacts connected...

That's the manufacturer's recommended connection (Eaton, who we use most, at least) Actually, it might only be applicable to electronic overloads, which I know monitor current in all phases and will detect a current imbalance and shut down if one leg is not drawing current. Traditional starters may not do this and you can get away with it, although I was pretty certain they all would, because an O/L on one phase without opening the other legs would single phase the motor.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,238
Location
Modesto, CA
That's the manufacturer's recommended connection (Eaton, who we use most, at least) Actually, it might only be applicable to electronic overloads, which I know monitor current in all phases and will detect a current imbalance and shut down if one leg is not drawing current. Traditional starters may not do this and you can get away with it, although I was pretty certain they all would, because an O/L on one phase without opening the other legs would single phase the motor.

O thats right. I forgot about the phase monitoring on solid state OLs. U can turn that off on some brands though. And most heater/conventional OLs dont have that!

Looks like I need to run a rotary phase converter. The motor on there now is about $2,000 and is a baulder motor. The Maximum amps it requires is 30AMPso I will need to pick one of those up. I can't run a single phase motor on this unit, the magnetic starter is all three phase. To replace that I would be spending a lot of money. The air compressor was a really good but, picked it up for $200.

Also, this will be the only piece of machinery that will require three phase. I don't think down the road we will ever get into machinery.

http://www.ebay.com/itm/5-HP-ROTARY...607?pt=LH_DefaultDomain_0&hash=item45fa633b0f

Bib Overalls: Those looks like really good buys, thanks!

If the motor has an FLA of 30a @ 240v 3phase, then its probably a 10hp motor!!
 
Last edited:
OP
B

bannerd

Well-known member
Joined
Nov 14, 2011
Messages
209
Location
Upstate NY
Ordered me a single phase motor, for the money to do a rotary I would have too much invested. Should be here on Monday, 70lbs electic brute :bounce:
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
You may have to replace the mag starter if the existing starter is a NEMA size 1, it's too small for a 5 HP 1Ø motor.
 