I live east of the Mississippi, and have dealt with :
345,000
138,000
69,000
34,500
13,800
12,470/7200
6600
4160
2400
480/277
240/120
208/120
But I've never heard of 240/416.![]()
Actually only used by the military, IIRC... It is one of the settings on my generator set.
For anyone willing to search for it, I did post an explanation why 120/208 exists with a graph showing why it is not 120/240. I remember that a few did complement the post saying it cleared up why it was that way.
BTW, with a wye configuration, you get two voltages with a neutral. With a pure delta, you get one voltage with no neutral. With a high-leg delta you get two voltages, with a neutral, but the neutral's relationship is to only one phase, not all three. A high-leg delta is not (usually) practical for a generator set as it is inherently unbalanced. The power company can do it because they typically have multiple customers using the configuration across the different phases.