3 phase solar

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
I have 360 v being produced line to line 3 phase .. line to neutral is 208. This is being produced by three Growatt 5000US solar spf inverters set up for three phase. Problem is the well pump is 3 phase 240v line to line.
Any help would be appreciated
 

Attachments

  • 12DB0C62-B098-4369-A88B-7606686A22BC.jpeg
    12DB0C62-B098-4369-A88B-7606686A22BC.jpeg
    461.5 KB · Views: 63
  • CF3A8ACE-4AF6-493F-AC2F-7C1553746B8A.jpeg
    CF3A8ACE-4AF6-493F-AC2F-7C1553746B8A.jpeg
    653.2 KB · Views: 66
  • 27639AB5-AABD-4722-B041-A6931983D5A2.jpeg
    27639AB5-AABD-4722-B041-A6931983D5A2.jpeg
    694.4 KB · Views: 67
  • A10EF740-C2FD-4904-BD90-6D85CC0D077A.jpeg
    A10EF740-C2FD-4904-BD90-6D85CC0D077A.jpeg
    666.7 KB · Views: 63
  • EF662206-1A1B-46F7-BE74-178F25A95C43.jpeg
    EF662206-1A1B-46F7-BE74-178F25A95C43.jpeg
    723.3 KB · Views: 59
  • D45E7E85-A5F3-4A14-B8A2-CF4DCEEBA90B.jpeg
    D45E7E85-A5F3-4A14-B8A2-CF4DCEEBA90B.jpeg
    571.2 KB · Views: 56
  • 1F42A329-68D2-4328-8C24-95364F70B307.jpeg
    1F42A329-68D2-4328-8C24-95364F70B307.jpeg
    715.1 KB · Views: 54
  • 6ADD28E7-A7BD-4450-91CE-728C19B3AFF0.jpeg
    6ADD28E7-A7BD-4450-91CE-728C19B3AFF0.jpeg
    760.4 KB · Views: 53
  • E08FAAE4-CA97-4258-8622-A9778A1BD1FE.jpeg
    E08FAAE4-CA97-4258-8622-A9778A1BD1FE.jpeg
    645.1 KB · Views: 61
  • 1FF3072E-FA83-425F-8A46-725A6D5A207B.jpeg
    1FF3072E-FA83-425F-8A46-725A6D5A207B.jpeg
    426.5 KB · Views: 72
To avoid these ads, REGISTER NOW!
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
First off where are you located? 360v is not a US 3 phase or single phase voltage.
This power is created via growatt 3 inverters 5000US in 3 phase (1 in each phase) config. Did you see the multimeter pics? I'm in Southern California sdge utility. My 3 phase well pump runs off utility 240 (120,120,209 line to neutral, 240 line to line).
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
Do not close any cb's in that panel with the inverter output connected.

Post a pic of the inverter nameplate.
 
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
Do not close any cb's in that panel with the inverter output connected.

Post a pic of the inverter nameplate.
Everything is disconnected via disconnect switch. Growatt spf 5000US I have three of them 1 in each phase each connected with communication cabling
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,408
Location
VT
No offense, but I don't think you should be messing around in that panel. Seeing tools propped up that close to exposed terminals that should have 480v seems careless.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,425
Location
Richmond, VA
Do you understand the risks with 480v 3 phase?


Also I just scanned the inverter specs. I missed where it says 3 phase output or output above 240v
Its in the manual, you can config sets of 3 for 3 phase. The output over 240v is why I believe it's a config issue

Why do you think that is a 480v panel?
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
Shut down all inverters. I'd "prefer" to have the 2nd and 3rd inverters to have disconnected outputs.
Check LCD settings #8 and #9 when the remaining inverter is in STANDBY mode.

#8 controls output voltage. 240/230/208v.
#9 controls frequency. 50/60 hz.


1729025424236.png
 
To avoid these ads, REGISTER NOW!
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
Are these 3 inveters hooked up L-L or L-N?
Each inverter in single phase (before being hooked up 3phase) has 3 output G,N,L .. essentially two hots and a ground. Growatt specify I hooked up a common wire between the three neutral lines and ground it. .. so my multimeter read 208 to neutral but 360 line to line
 
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
Two other things to check:
1729025815045.png

This is configuration for 3-phase:
1729025743822.png
I see that. The pictures I included show I've set that feature to 209 not 230. If I go back and reset the features to 230 .. I'm going to end up with over 400 v line to line
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
So you are connected exactly as per diagram in 5.5 ?

Diagram does not show a neutral to be grounded. This is a safety issue where the grounded surfaces will carry current.
Each inverter in single phase (before being hooked up 3phase) has 3 output G,N,L .. essentially two hots and a ground. Growatt specify I hooked up a common wire between the three neutral lines and ground it. .. so my multimeter read 208 to neutral but 360 line to line
 
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
Two other things to check:
1729025815045.png

This is configuration for 3-phase:
1729025743822.png
I see that. So what should the actual output s
Shut down all inverters. I'd "prefer" to have the 2nd and 3rd inverters to have disconnected outputs.
Check LCD settings #8 and #9 when the remaining inverter is in STANDBY mode.

#8 controls output voltage. 240/230/208v.
#9 controls frequency. 50/60 hz.


1729025424236.png
the remaining inverter if disconnected from 3 phase will be 230-240 output with two hots .. but my motor is three phase 240.. are you saying single phase 240v can run 3 phase 240v motor
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
I see that. The pictures I included show I've set that feature to 209 not 230. If I go back and reset the features to 230 .. I'm going to end up with over 400 v line to line
I'm not that familiar with 3-phase, but it looks to me like more than 240V should not be possible across any L1/L2/L3.

1729028166857.png

the remaining inverter if disconnected from 3 phase will be 230-240 output with two hots .. but my motor is three phase 240.. are you saying single phase 240v can run 3 phase 240v motor
You should not run a 240V 3-phase motor on 2 phase power no.

I assume this is the "US spec" inverter bought from a semi-reliable importer (Signature Solar, etc) - not something you've bought "off the boat"?

Is this grid tie or straight inverter power from battery?
 
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
So you are connected exactly as per diagram in 5.5 ?

Diagram does not show a neutral to be grounded. This is a safety issue where the grounded surfaces will carry current.
Ac out inverter source Neutral grounded
 

Attachments

  • 4274114A-9EA6-4097-A690-DB46791254B8.jpeg
    4274114A-9EA6-4097-A690-DB46791254B8.jpeg
    782 KB · Views: 54
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
I'm not that familiar with 3-phase, but it looks to me like more than 240V should not be possible across any L1/L2/L3.

1729028166857.png


You should not run a 240V 3-phase motor on 2 phase power no.

I assume this is the "US spec" inverter bought from a semi-reliable importer (Signature Solar, etc) - not something you've bought "off the boat"?

Is this grid tie or straight inverter power from battery?
Straight from solar panels and 600 amp hrs of 48 v LiFePO4 .. from signature solar
 
OP
S

snowmaneu1

Well-known member
Joined
Oct 15, 2024
Messages
70
I'm not that familiar with 3-phase, but it looks to me like more than 240V should not be possible across any L1/L2/L3.

1729028166857.png


You should not run a 240V 3-phase motor on 2 phase power no.

I assume this is the "US spec" inverter bought from a semi-reliable importer (Signature Solar, etc) - not something you've bought "off the boat"?

Is this grid tie or straight inverter power from battery?
I have three hots no neutral
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
Ac out inverter source Neutral grounded
Terminology is everything. You connected each inverter to a neutral. The neutral is bonded to ground elsewhere, you did not ground the neutral a second time b/c of the inverters, correct?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
Is that sole black wire on the left vertical bar in the panel your neutral for the inverters?
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,771
Location
Southern Oregon
Each inverter in single phase (before being hooked up 3phase) has 3 output G,N,L .. essentially two hots and a ground. Growatt specify I hooked up a common wire between the three neutral lines and ground it. .. so my multimeter read 208 to neutral but 360 line to line
That actually makes sense, math wise. 208 * 1.73 = approx 360

Its just not a conventional 3p voltage configuration.

1729029667225.png

Will your pump run on 208V-3p? A lot of stuff is rated 208-230.

Problem is the well pump is 3 phase 240v line to line.
Where are you measuring that at? At the control box L1,L2,L3? Measure L1-L2, L1-L3, L2-L3.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
This power is created via growatt 3 inverters 5000US in 3 phase (1 in each phase) config. Did you see the multimeter pics? I'm in Southern California sdge utility. My 3 phase well pump runs off utility 240 (120,120,209 line to neutral, 240 line to line).
yeah so your inverters are not configured or connected properly.

FYI those breakers are not rated for more than 240v. you should shut off the inverters before doing any other work :shocking:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I'm not that familiar with 3-phase, but it looks to me like more than 240V should not be possible across any L1/L2/L3.

1729028166857.png


You should not run a 240V 3-phase motor on single phase power no.

I assume this is the "US spec" inverter bought from a semi-reliable importer (Signature Solar, etc) - not something you've bought "off the boat"?

Is this grid tie or straight inverter power from battery?
fixed it for you. 2 phase is something entirely different
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I have three hots no neutral
is this a grid tied system?

If so what is the voltage of the utility? 240v 3Ø? if so then you have delta service 3 wire.

how do you have your inverters connected to utility? 1 line from each inverter goes to utility connection along with neutral. 1 line from each inverter goes to house load.
 
Last edited:

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,408
Location
VT
that is NOT a 480v panel. notice the breakers are rated 240v?
No, I didn't.

Seems the OP shouldn't be getting 480v anyway, not sure how he's getting 360v

Either way seems he's in over his head with some potentially dangerous voltages.
 