When I set each inverter in the three phase setup to 208v, I get 208v l-n and 360 L-L. These are 48 v inverters.If the OP connected 3 inverters with a common connection and then has 3 legs hot, he has it configured in a "wye" configuration.
Currently he must have the output of each inverter set to 208V. This would create a system of 208V L-N and 360V L-L.
In order to get 240V L-L, he needs the output set to 138.7V in a "wye" configuration ( this output is not possible with this inverter)
Set the Inverter to 208V output, L-L config and get 2 - 32V secondary, "boost" transformers, wired in an open delta, to boost from 208 to 240 ( *** edit: I just remembered that these inverters cannot be set to 120V. In that case you are SOL )

solar if he closes that disconnect