3" underground conduit question

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,746
Location
Northeastern CT
When the power company representative spoke to me about the underground conduit, he told me that 3" PVC was ok from the meter socket out to the pole; however, he wants a metal long sweep where it goes up the pole, and that sweep needs to be grounded to the ground rod at the pole. From the sweep, he said I can use PVC going up the pole.
I just don't understand why the long sweep needs to be metal and why it needs to be grounded. The only thing that I can think of is that it might be easier to pull the wire through. It is the grounding that has me baffled. Could you explain this to me? thanks
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,313
Location
NJ
The metal sweep is so your pull rope doesn't cut through the inside radius. When pulling tension is high ( long run, lots of bends) it can happen. For simple runs I wouldn't bother. However, POCO rules so just do it.

The grounding is to ensure the sweep has better contact with wet(ter) soil (yeah, I know!)
Also ensures a low resistance path back to the xformer neutral that it could take out the fuse on line side if fault occurs.
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
Plastic bends can rub through when pulling wire.

If it's buried deep enough the nec has no requirement to ground it. But it's the power company's conduit so they have the ultimate say
 