3-way switch and wire guage questions

Mike83

Well-known member
Joined
Jan 24, 2008
Messages
2,156
Location
Wisconsin
I started installing a ceiling fan yesterday (new location) and I planned to pull power from an existing switch. Well, to my dismay I find out you cannot in any way I know of pull power from the leg end of a 3-way switch due to the traveller wires changing from hot to neutral. I can pull power from the garage since the other side of the wall of the family room is the garage, but that would be a 20 amp circuit and I already spent an unreal amount of effort pulling 14-ga wire from the switch location to the box in the ceiling by crawling in the attic.

So, my two questions:

1) Is there any way I can get a constant hot supply to my fan switch with only the leg end 3-way switch next to it?

If not:

2) Can I use the 14 ga wire already installed for the fan if I pull power from the 20 amp garage circuit (the 14 ga would only exist from the switch to the fan). Could I maybe just downgrade the breaker to 15 amp as a last resort? Fwiw I don't use anything that pull more than 13 amps from the garage circuit now but in consideration of future use would this be feasible?

Thanks for the help and hopefully I make sense with my explanation. This project has become bigger than I imagined.
 
To avoid these ads, REGISTER NOW!

ArthurPE

Banned
Joined
Jun 14, 2009
Messages
423
a 3 way switch does not switch H and N...
the travellers run between the switched legs and depending how it's wired, and which 3 way you are wired to, you may have a constant 120 leg...
the neutral is often available at the switch (although is passes thru and is not used)

if you draw 13A I would not go to a 15A, it's supposed to be oversized by 25%...

a couple of examples:
power at load
3wayswitch.jpg


power at switch
3-way-switch-wiring-diagram1.jpg


a bunch of drawings: http://images.google.com/images?hl=en&q=3 way switch diagram&um=1&ie=UTF-8&sa=N&tab=wi
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
you cannot supply a circuit containing 14ga wire from a 20a circuit. Your options (besides replace the wires) are replace the breaker with a 15a breaker (I would tag the wire inside the panel as needing a 15a breaker due to #14 in the circuit) or install a small 2 breaker subpanel with a 15a breaker in it (theyre cheap, like $12) where you tap into the garage circuit (the panel must be accessable) to protect the #14 wire at 15 amps.
 

hidollartoys

Well-known member
Joined
Jul 15, 2008
Messages
594
Location
K. C. Metro area
If you have a neutral "feed through" in the box that you have pulled the 14 ga to then yes but that circuit should be a 15 amp circuit as explaned by mrb.

Arthur, your second diaghram does not show a circuit with "power at switch". It shows "power at load".
 
Last edited:

ArthurPE

Banned
Joined
Jun 14, 2009
Messages
423
If you have a neutral "feed through" in the box that you have pulled the 14 ga to then yes but that circuit should be a 15 amp circuit as explaned by mrb.

Arthur, your second diaghram does not show a circuit with "power at switch". It shows "power at load".

cut and pasted wrong one...in a rush

3-way-switch-wiring-diagram.jpg
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
This is just in theory, not really advocating anything not code but if this 14 feeds a fixture with a known load and no way to plug anything in to it to overload the circuit then the real danger of using lighter wire in this circuit is minimal, similar to a fixture wire.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
This is just in theory, not really advocating anything not code but if this 14 feeds a fixture with a known load and no way to plug anything in to it to overload the circuit then the real danger of using lighter wire in this circuit is minimal, similar to a fixture wire.

true, but then you have an unrelated fire and your insurance co finds the #14 hooked to #12 and refuses to pay the claim due to illegal DIY wiring.

There is no reason to not do this right.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I find a lamp cord during a re-wire the other day, been in there 50 yrs on a switch loop and perform perfectly. No one knew it was there but the ins co gladly take premiums on this property all those years. I dont recall anywhere in my policy that says they wont ins anything that hasnt been inspected.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
I find a lamp cord during a re-wire the other day, been in there 50 yrs on a switch loop and perform perfectly. No one knew it was there but the ins co gladly take premiums on this property all those years. I dont recall anywhere in my policy that says they wont ins anything that hasnt been inspected.

they gladly take the premiums, and look for any reason to delay or avoid a payout. Happens all the time.
 