3 Way Valves

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,075
Location
Gotham City
Someone confirm....I was looking to put a 3 way Ball Valve inline....and split of cold to one direction and split off cold to another. The valve itself would just be a shutoff.

I cannot remember where but I believe it stated the 3 way valves are not meant for that sort of line-2 way split application. I cannot recall the specifics but it wasn't inferring it was a mixing, but just that for how I though a 3 way ball valve was, it could be used for how I intended. Something to the degree the handle orientation was meant to -temper- flow from port 1 vs port 2.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
To control temperature or flow rate you need a mixing valve. A three way ball valve is only to be used to change flow completely from one port to the other, I.E. allow flow from port A to B or A to C. It's not meant to split flow between B & C from A.

Tommy
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
M

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,075
Location
Gotham City
yes, I know what a mixing valve is. 10-4 on what the 3 Way days....confirmed what I read, which is not meant to -split-
 
Last edited:

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,932
Location
oregon
There are a few different configurations for a 3 way valve. This page https://www.industrialspec.com/about-us/blog/detail/three-way-ball-valve-t-port-l-port-flow-patterns shows most of them. It also depends on what you want to do with the valve.
One input with two outputs which you choose output one or two.
Two inputs and one output where you select which input.
These are the two most basic configurations of a 3 way valve.

From there you can go to a 5 port valve where when switched the off port is vented and then into other configurations that get more specialized.

lg
no neat sig line
 
OP
M

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,075
Location
Gotham City
Thx Larry. No need to over-comlpicate the-valve-install. The place where I'm going to either end up sweating or IPS....is just tight/dense. For the application, where I would need 2 outputs off this *shutoff*, figuered the 3 way was the obvious choice.

Based on the other posts, it did confirm my origina inquiry that 3 ways were not meant for that app ?
 