Forgive the long "background" section; my actual question is down a bit, but I want to minimize confusion since this conversation could easily go sideways. Everyone please try to make it clear what part of the question you're contributing to.
In my single-man home shop the general purpose 240v circuits each have two receptacles (the two receptacles are never used at same time). All the circuits are run with 3X 10 ga THHN (red, black, and green ground) in 1" emt conduit and currently have 20a receptacles and breakers.
I want to bring 240v + 120v to my tablesaw workstation that is about 12ft from the nearest wall. The 120v will power the router station and a general use outlet or two. Two separate commercial electricians have both come-up with the same solution using a multi-wire branch circuit:
1. add a neutral (white) to the circuit feeding the receptacle nearest the saw to make it 120/240v with a L14-20 receptacle
2. run a 10ga SJOW "cord" from the L14-20R to a box mounted to the saw workstation
3. In the box at the workstation, the red, black, and ground would connect to a 20a 240v receptacle (L6-20), while the black, white, and green would connect to a 20a 120v duplex receptacle.
QUESTIONS: Up to this point, the two electricians are in agreement and it all makes sense to me. There are two points the electricians disagree on:
1) one says that we only need to run the 4th (white) wire to the receptacle that will bring 120v to the workstation, NOT the second receptacle that is on the same circuit. The other insists the white would also need to be run to the 2nd receptacle even though it would just be capped in the box.
Adding a white to the conduit leading to the 2nd receptacle on the circuit could (depends on question 2 below) force us to use a 70% derating instead of the current 80%, which would mean the 10 ga wires would no longer be able to be used for a 30a circuit. One of the other circuits in the conduit is currently 30a and I'd like to keep it as an option for all the "general purpose" 250v circuits.
This brings us (finally!) to the 2nd QUESTION: the electrician suggesting the white needs to also be run to the 2nd receptacle on the circuit says that derating isn't an issue because the white doesn't count as a current carrying conductor on this circuit. The other electrician says that it would indeed be counted as a CCC. I know this can get confusing, so wanted to get some additional opinions.
Thanks for any help and sorry again for the long post.
In my single-man home shop the general purpose 240v circuits each have two receptacles (the two receptacles are never used at same time). All the circuits are run with 3X 10 ga THHN (red, black, and green ground) in 1" emt conduit and currently have 20a receptacles and breakers.
I want to bring 240v + 120v to my tablesaw workstation that is about 12ft from the nearest wall. The 120v will power the router station and a general use outlet or two. Two separate commercial electricians have both come-up with the same solution using a multi-wire branch circuit:
1. add a neutral (white) to the circuit feeding the receptacle nearest the saw to make it 120/240v with a L14-20 receptacle
2. run a 10ga SJOW "cord" from the L14-20R to a box mounted to the saw workstation
3. In the box at the workstation, the red, black, and ground would connect to a 20a 240v receptacle (L6-20), while the black, white, and green would connect to a 20a 120v duplex receptacle.
QUESTIONS: Up to this point, the two electricians are in agreement and it all makes sense to me. There are two points the electricians disagree on:
1) one says that we only need to run the 4th (white) wire to the receptacle that will bring 120v to the workstation, NOT the second receptacle that is on the same circuit. The other insists the white would also need to be run to the 2nd receptacle even though it would just be capped in the box.
Adding a white to the conduit leading to the 2nd receptacle on the circuit could (depends on question 2 below) force us to use a 70% derating instead of the current 80%, which would mean the 10 ga wires would no longer be able to be used for a 30a circuit. One of the other circuits in the conduit is currently 30a and I'd like to keep it as an option for all the "general purpose" 250v circuits.
This brings us (finally!) to the 2nd QUESTION: the electrician suggesting the white needs to also be run to the 2nd receptacle on the circuit says that derating isn't an issue because the white doesn't count as a current carrying conductor on this circuit. The other electrician says that it would indeed be counted as a CCC. I know this can get confusing, so wanted to get some additional opinions.
Thanks for any help and sorry again for the long post.