30 amp breaker issues
steamboat
Kansas City, Missouri
Just purchased a Wilton 3" X 79" belt sander. Motor is 4HP, 220 volt, 3 phase at 3456 RPM, 15.2 amps. I had a static phase converter 4 to 8 HP and attached it to the machine. I'm running 10/3 wire with a 30 amp breaker. The belt sander will start up without any issues and run strong for 30 seconds or so and then trip the breaker. Not sure if I need to run heavier wire and increase the breaker to a 40 or 50 amps. I didn't think the start up on the machine would be double the 15.2 amps and trip the 30 amp breaker. Is there any alternative to running the larger wire and breaker.
Norcal
Motor rules are different then "normal" branch circuits, & it may be fine to use a larger breaker then would be normal, but if NM cable (Romex) is used it has to be used at the 60 degree C ampacity, another thing is your static converter just starts the motor, after that it single phases, a rotary phase converter would be a better choice & then the 1/3 of the HP loss that happens w/ a static converter is not a problem.
steamboat
I had a rotary phase converter and sold it with another machine. I see now that was foolish. But I am running romex 10/3 wire and is dedicated to that 220 plug in. Nothing else draws on that line except what I plug in. Can I get away with putting on a 40 amp breaker and see if the motor will run without tripping the large breaker. I don't have a Clamp on ammeter to test the converter. If I have to run heavier wire I will, but not looking forward to it.
steamboat
Should of mentioned the phase converter can be changed from a 4 HP setting to a setting that allows up to 8 HP. The manual states if the motor will run not on the 4 HP setting, change it to the up to 8 HP setting. Never tried the 4 HP setting the converter can prewired on the up to 8 HP setting. Not sure if a change to the 4 HP if that would make any difference at this point.
As Norcal already pointed out, a breaker feeding NM wire is sized on the 60c deg column so no u cant put a larger breaker on that 10/3. Also, breakers for motors are sized at 300% of FLC, which u would have to look up as i dont have my code book in front of me!
steamboat
Sorry for not picking up on that right away. Looks like a 50 amp breaker is going in. I could have used a larger breaker on numerous other occasions. Any suggestions on romex or another type.
Yes, wire is sized at 125% of FLC and unfortunately, my books are at work so i cant size the wire for u. But i know pattenp or another sparky on here will be able to.
lametec
3 phase amps are not the same as single phase amps.
If the motor draws 15.2A on 3 phase, it will draw 26.3A from the single phase supply. This is an "ideal" conversion, though, and the fact that you're using a static converter probably skews the numbers a bit.
Not that it should draw anywhere near 15.2A idling.
A rough rule of thumb is that a 3 phase motor running through a phase converter will draw about 3 time the amount of current. If it is a rotary phase converter, figure 4 times.
Thanks to all for the information. It really helped to figure out the issue. Not sure if I want to go with romex type of wire or another option.
So based on what theoldwizard said, u need a wire rated for 57a. 15.2*3=45.6*125%= 57a. You could use either #4 NM or #6 thhn individual wire in conduit!