30 Amp disconnect for Water Heater

steel billet

Member
Joined
Nov 6, 2012
Messages
7
Would there be any issues if I replaced my 30 amp water heater disconnect with one that has a 15 amp GFCI in the box? I don't have a receptacle on that side of the basement. Just thinking of a easy way to get some power over there. Could it damage the thermostat?
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,372
Location
Michigan
All like that i've seen need a separate15 amp circuit to power the gfci.

Sent from my C771 using Tapatalk 2
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
It's pretty much a sure thing that you only have a 240V circuit to your water heater. Meaning you CANNOT tap a 120V circuit off it since there is no neutr4al present.

IF you have a neutral and ground present, along with the two hots, you could use a small panel with a separate 15 or 20A breaker feeding the GFI. You CANNOT have the GFI off the 30A circuit alone.
 
OP
S

steel billet

Member
Joined
Nov 6, 2012
Messages
7
juzasede.jpg

I was looking at this bit in a 30amp. This 60amp disconnect has a 20amp GFI.
 
To avoid these ads, REGISTER NOW!

Bmwsyc

Well-known member
Joined
Dec 1, 2013
Messages
49
Says on the box that the gfi and 240 volt load are wired separately. If you drag a 15 amp 120 volt circuit over there, it would be fine.
 