I am running a 240 volt line in my detached garage for welder, compressor and a kitchen range I plan to use for powder coating. I was originally planning to run a 50 amp circuit. However looking at the current draw, it is 22 amps for the welder I plan to buy (which actually has a 50 amp plug on it) and 15 amps for the compressor plan to buy. My concern is that a 50 amp breaker won't provide adequate protection for the actual devices. Also I can't find wire nuts for 6 gauge wires locally (split bolt with electrical tape?) whereas I can use 10 gauge wire for a 30 amp circuit. What to do?
Another reason I was considering running a 50 amp circuit was to possibly run a stick welder. I probably won't need to if I buy this MIG, but I did pick up an old Craftsman 250 amp stick welder that says I should be on an 80 amp breaker. I only have 60 amps going out to the garage, and modern receptacles are only rated for up to 50 amps anyway. Outdated wiring procedures I am guessing, has me scratching my head though.
Any input is much appreciated.
Another reason I was considering running a 50 amp circuit was to possibly run a stick welder. I probably won't need to if I buy this MIG, but I did pick up an old Craftsman 250 amp stick welder that says I should be on an 80 amp breaker. I only have 60 amps going out to the garage, and modern receptacles are only rated for up to 50 amps anyway. Outdated wiring procedures I am guessing, has me scratching my head though.