I have a 30 amp circuit breaker in my main electric panel that I want to tap into, but only run 15 amp receptacles off of it. Is there a safe way to do this. My only other circuit breaker is 50 amp.
 
To avoid these ads, REGISTER NOW!

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
Is the breaker in use or spare? Assuming spare, replace the breaker with a 15 or 20 amp depending on wire size for the receptacles you want to run #14 you can use a 15 amp #12 you can use a 15 or 20 amp breakers.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
What do you mean by "tap into?" Is this breaker already feeding some piece of equipment, and you want it to ALSO feed these receptacles?

And you're saying that the only other breaker in the entire panel is a 50 amp breaker? What does that breaker feed? There are no other spaces available in the panel to add more breakers? Pics of the panel would help.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
You are not going to be able to post pictures until you have a few more posts. Do a few more posts on other threads, I think you need 5, then you can post pictures. Is this a 2-pole breaker. Is it already feeding something. It doesn't really matter, you cannot do what you are asking. Only 30 amp receptacles can be on a 30 amp circuit. 210.21(B)(3) They do not make 30 amp duplex receptacles.

If this is a spare breaker, remove it and install a 15 or 20 amp breaker and run the correct size wire to the receptacles.

Is the panel full, if so, it may accept tandems. What is the make and model number of your panel.
 
Last edited:
OP
O

Onezubi

New member
Joined
Feb 17, 2021
Messages
2
Location
AZ
There are no empty circuit breakers. It was originally set up for a 30 amp and 50 amp rv hook up. They are both being used. When I get home I will post what brand of box it is. Thanks
 

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862
Tandem/split breakers should be an option for you to use to replace an existing breaker.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You are not going to be able to post pictures until you have a few more posts. Do a few more posts on other threads, I think you need 5, then you can post pictures. Is this a 2-pole breaker. Is it already feeding something. It doesn't really matter, you cannot do what you are asking. Only 30 amp receptacles can be on a 30 amp circuit. 210.21(B)(3) They do not make 30 amp duplex receptacles.

If this is a spare breaker, remove it and install a 15 or 20 amp breaker and run the correct size wire to the receptacles.

Is the panel full, if so, it may accept tandems. What is the make and model number of your panel.

Saying only 30 amp receptacles can be on a 30 amp circuit is not accurate. To clarify, 210.21(B)(3) applies only to multioutlet receptacles. 210.21(B)(1) is for single outlet receptacles and the amp rating is not to be less than the circuit, so actually you can put a larger amp rated receptacle on a lower amp circuit if it's a single outlet.
 

Wrench97

Well-known member
Joined
Jun 23, 2018
Messages
12,401
Location
Southeastern Pa
Strange to see a 30a single breaker, let alone a 50a single.

So you will need to remove a single breaker and install 2 half size breakers sometimes called 1/2"/Half size or splits 2 of these fit where 1 standard is removed. You will need to know the correct brand and type that you have now.

12inchBreaker.JPG
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Saying only 30 amp receptacles can be on a 30 amp circuit is not accurate. To clarify, 210.21(B)(3) applies only to multioutlet receptacles. 210.21(B)(1) is for single outlet receptacles and the amp rating is not to be less than the circuit, so actually you can put a larger amp rated receptacle on a lower amp circuit if it's a single outlet.

He is talking about multiple receptacles, so 210.21(B)(3) does apply. This is not for a single receptacle. I said only 30 amp receptacles on a 30 amp circuit, I didn't say only a 30 amp receptacle on 30 amp circuit. What I said is accurate. If you remove that "s" from receptacles, it changes the whole meaning ;)
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
He is talking about multiple receptacles, so 210.21(B)(3) does apply. This is not for a single receptacle. I said only 30 amp receptacles on a 30 amp circuit, I didn't say only a 30 amp receptacle on 30 amp circuit. What I said is accurate. If you remove that "s" from receptacles, it changes the whole meaning

Sorry the "S" didn't equate to me since under IRBC multiple outlets on a 30A or greater circuit isn't allowed. I know the IRBC isn't adopted everywhere but is widely followed. So when speaking of 30A receptacles it is usually a single dedicated outlet. That's where my head was.
 

Wrench97

Well-known member
Joined
Jun 23, 2018
Messages
12,401
Location
Southeastern Pa
He is talking about multiple receptacles, so 210.21(B)(3) does apply. This is not for a single receptacle. I said only 30 amp receptacles on a 30 amp circuit, I didn't say only a 30 amp receptacle on 30 amp circuit. What I said is accurate. If you remove that "s" from receptacles, it changes the whole meaning ;)

Sorry the "S" didn't equate to me since under IRBC multiple outlets on a 30A or greater circuit isn't allowed. I know the IRBC isn't adopted everywhere but is widely followed. So when speaking of 30A receptacles it is usually a single dedicated outlet. That's where my head was.


How homes do either of you know of with 30a 110v receptacles?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
How homes do either of you know of with 30a 110v receptacles?

Wait a minute. Wasn't your question a troll question?

An "Internet troll" or "Forum Troll" is a person who posts outrageous message to bait people to answer. Trolls delight in sowing discord on the forums. A troll is someone who inspires flaming rhetoric, someone who is purposely provoking and pulling people into flaming discussion.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Neither one of you are any help to op more like trolls:lol_hitti

It seems to me that the op asked a electrical question about doing something and if it would be safe. We answered that question and told him that it would be a violation of the NEC. Even gave him options like changing the breaker if possible or adding a sub panel. You on the other hand suggested installing a "thin" breaker in post #9. The only panel that uses these, to my knowledge are GE. Also old FPE had them also. What if he doesn't have a GE. Tandem breakers are a different story, but the panel has to be listed to accept them
 