With the help of gj, I wired a 50 amp circuit a few years back. This was done using 6/3 just in case I needed the other wire. I put a Leviton ms602 switch on this circuit near the outlet to have a shutoff. Since I am moving, I'd like to take this expensive switch with me and want to know if I can put a 30a switch in its place.
I have a Leviton ms302, 30a that says is good for 5hp at 240v. That is fine for this circuit. I also have a 30a Seymour Pass that has no info. Is it safe to assume it's rated the same?
Also, the Leviton has line coming in from the left side and to the motor on the right side of the switch if you are looking at the switch from the front. The Seymour Pass has no markings. Is is standard to have line in from left and motor on right?
Thanks for the help.
I have a Leviton ms302, 30a that says is good for 5hp at 240v. That is fine for this circuit. I also have a 30a Seymour Pass that has no info. Is it safe to assume it's rated the same?
Also, the Leviton has line coming in from the left side and to the motor on the right side of the switch if you are looking at the switch from the front. The Seymour Pass has no markings. Is is standard to have line in from left and motor on right?
Thanks for the help.