Is that because you should not wire a circuit with more than 80% of the breaker capacity. This said, a 60A breaker should not have more than 48A of juice and anything between 55-60 is probably going to be momentary and pop it as it'd be a failure of some component?
Not quite. A 60 amp breaker will pass 60 amps indefinitely. (With the possible exception of one located in a very hot environment). The circuit derating is an exercise in conservative use - allows for peak currents for inductive loads, etc. The 60 amp breaker allowed in this case is because there is no commercially available 55 amp breaker. In most calculations the NEC allows rounding up to the next readily available size.