I am in the process of building a new home and separate workshop. I am coming across issues when figuring out how to run the wiring due to location the power is coming onto the lot. It will be less than 100 feet to the garage but approximately 350' to the house.
Utility service Poles will be feeding transformer (pole mount).
I have a couple options and would like to get feedback on the best option from others experienced with this more than I.
I believe I can:
1)mount the meter remotely - close to the utility pole and run each service from there.
2) mount on garage and split out from there
3) Mount meter remotely closer to the house within 100' and garage would be close to the same.
Garage and house are in similar directions from where the power will be coming onto the land. Garage is obviously closer to incoming power.
Stipulation with the serving power company, the total capacity of disconnects can not exceed 300A and no buss fusing more than 300A. Only equipment approved is a standalone meter - no combo panels are approved.
The biggest question I have: Is there a way to legally get power from the remote meter to a 200A panel to the house and 100A panel to the workshop?
Would mounting on the workshop make it an easier way to split the power?
Local authority is subject to 2017 NEC
I understand most of the basic requirements for electrical install and they allow homeowners to wire primary homes after a test is taken and passed.
Thanks.
Utility service Poles will be feeding transformer (pole mount).
I have a couple options and would like to get feedback on the best option from others experienced with this more than I.
I believe I can:
1)mount the meter remotely - close to the utility pole and run each service from there.
2) mount on garage and split out from there
3) Mount meter remotely closer to the house within 100' and garage would be close to the same.
Garage and house are in similar directions from where the power will be coming onto the land. Garage is obviously closer to incoming power.
Stipulation with the serving power company, the total capacity of disconnects can not exceed 300A and no buss fusing more than 300A. Only equipment approved is a standalone meter - no combo panels are approved.
The biggest question I have: Is there a way to legally get power from the remote meter to a 200A panel to the house and 100A panel to the workshop?
Would mounting on the workshop make it an easier way to split the power?
Local authority is subject to 2017 NEC
I understand most of the basic requirements for electrical install and they allow homeowners to wire primary homes after a test is taken and passed.