Power and Control Tray Cable: Type TC
I. General
336.1 Scope. This article covers the use, installation, and
construction specifications for power and control tray cable,
Type TC.
336.2 Definition.
Power and Control Tray Cable, Type TC. A factory assembly
of two or more insulated conductors, with or without
associated bare or covered grounding conductors, under
a nonmetallic jacket.
II. Installation
336.10 Uses Permitted. Type TC cable shall be permitted
to be used as follows:
(1) For power, lighting, control, and signal circuits.
(2) In cable trays.
(3) In raceways.
(4) In outdoor locations supported by a messenger wire.
(5) For Class 1 circuits as permitted in Parts II and III of
Article 725.
(6) For non–power-limited fire alarm circuits if conductors
comply with the requirements of 760.49.
(7) In industrial establishments where the conditions of
maintenance and supervision ensure that only qualified
persons service the installation, and where the cable is
continuously supported and protected against physical
damage using mechanical protection, such as struts,
angles, or channels, Type TC tray cable that complies
with the crush and impact requirements of Type MC
cable and is identified for such use with the marking
Type TC–ER shall be permitted between a cable tray
and the utilization equipment or device. The cable shall
be secured at intervals not exceeding 1.8 m (6 ft).
Equipment grounding for the utilization equipment
shall be provided by an equipment grounding conductor
within the cable. In cables containing conductors
sized 6 AWG or smaller, the equipment grounding conductor
shall be provided within the cable or, at the time
of installation, one or more insulated conductors shall
be permanently identified as an equipment grounding
conductor in accordance with 250.119(B).
Exception: Where not subject to physical damage, Type
TC-ER shall be permitted to transition between cable trays
and between cable trays and utilization equipment or devices
for a distance not to exceed 1.8 m (6 ft) without
continuous support. The cable shall be mechanically supported
where exiting the cable tray to ensure that the minimum
bending radius is not exceeded.
(8) Where installed in wet locations, Type TC cable shall
also be resistant to moisture and corrosive agents.
Informational Note: See 310.15(A)(3) for temperature
limitation of conductors.
336.12 Uses Not Permitted. Type TC tray cable shall not
be installed or used as follows:
(1) Installed where it will be exposed to physical damage
(2) Installed outside a raceway or cable tray system, except
as permitted in 336.10(4) and 336.10(7)
(3) Used where exposed to direct rays of the sun, unless
identified as sunlight resistant
(4) Direct buried, unless identified for such use.
336.24 Bending Radius. Bends in Type TC cable shall be
made so as not to damage the cable. For Type TC cable
without metal shielding, the minimum bending radius shall
be as follows:
(1) Four times the overall diameter for cables 25 mm
(1 in.) or less in diameter
(2) Five times the overall diameter for cables larger than
25 mm (1 in.) but not more than 50 mm (2 in.) in
diameter
(3) Six times the overall diameter for cables larger than
50 mm (2 in.) in diameter
Type TC cables with metallic shielding shall have a
minimum bending radius of not less than 12 times the cable
overall diameter.
336.80 Ampacity. The ampacity of Type TC tray cable
shall be determined in accordance with 392.80(A) for 14
AWG and larger conductors, in accordance with 402.5 for
18 AWG through 16 AWG conductors where installed in
cable tray, and in accordance with 310.15 where installed in
a raceway or as messenger-supported wiring.
III. Construction Specifications
**snip**
336.104 Conductors. The insulated conductors of Type TC
cables shall be in sizes 18 AWG to 1000 kcmil copper, nickel,
or nickel-coated copper, and sizes 12 AWG through 1000 kcmil
aluminum or copper-clad aluminum. Insulated conductors
of sizes 14 AWG, and larger copper, nickel, or nickel-coated
copper, and sizes 12 AWG through 1000 kcmil aluminum or
copper-clad aluminum shall be one of the types listed in Table
310.104(A) or Table 310.104(B) that is suitable for branch
circuit and feeder circuits or one that is identified for such use.
**snip**
336.116 Jacket.
**snip**
336.120 Marking.
**snip**