4-wire power to 3-wire receptacle

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,101
Location
Marina del Rey
Need to hookup an adapter for temporary jobsite power to Miller Dynasty 200DX. Available is 50-amp, 230-volt, 4-wire receptacle. Welder has 50-amp, 230-volt, 3-wire plug. Should the center pin of the adapter's 3-wire receptacle be connected to neutral (white) or ground (green) or both? Maybe a dumb question, but just want to be safe.
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
You would just need the 2 hots and the ground going to the welder receptacle, no neutral. The U shaped/ round pin on the 4-wire receptacle is the ground. You better change 230 to 240 volts in your post, some people will jump on you about that.
 
Last edited:
OP
E

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,101
Location
Marina del Rey
Jobsite receptacle looks like this. Is wired single phase. Ground is outer housing.

41avP0g1UKL._SY445_.jpg
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Just out of curiosity,,, is this a main panel or a sub? Another curiosity, I am not familiar and cant remember them all but what is that recept?
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Nother curiosity, how heavy of a weld you got to make? I assume the center pin is the ground and bonded to the yoke.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
E

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,101
Location
Marina del Rey
Tig welding 0.083" and 0.065" wall thickness stainless tubing. Already committed to adapting power to 230-volts receptacle.
 

Kevin Essiambre

Well-known member
Joined
May 1, 2014
Messages
208
Location
Ottawa, Ontario, Canada
OP, you are correct that the outside is the ground on that receptacle. I've attached a photo for reference.

To go from the 50 amp 125/250 twist lock to your 6-50 receptacle you need, you'll connect the ground to ground. X and Y are your power terminals on the plug and receptacle. Ignore the W terminal, that is for the neutral which you won't need.

I'd make a nice adapter cord, maybe 10' long with 6awg cable with the right ends for the cable. Then you'll have one for future use. Or, with 10' of cord, you could just keep changing the male end to whatever plug you need. Either way, it's handy to have adapters for different receptacles. 1c4b66db53f44c485922da900c90700a.png
 

Attachments

  • 1c4b66db53f44c485922da900c90700a.png
    1c4b66db53f44c485922da900c90700a.png
    1.8 KB · Views: 0
Last edited:

AngryBeaver

Well-known member
Joined
Jul 12, 2017
Messages
1,705
Location
Lake Milton Ohio
Kevin is right, except you have a CS8364 plug. the two with the tabs inboard are the two hots. (x and Z) W is not needed on the welder. The center pin in for alignment purposes only

This is a very common plug on rental generators for single phase power and carry one of these adapters on my service truck for running my 200 amp tis/stick machine.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
Is the receptacle on a spider box? The CS locking receptacle & inlets are pretty much standard on them, usually have 1, 30A 240V receptacle, & a number of GFCI protected 20A 120V locking receptacles on them. As mentioned above, the plugs/receptacles/connectors are marked, most common CS locking brand is Marinco, probably cheaper, but I still prefer Hubbell.
 