Building a detached shop building, metal frame concrete slab. I have 4 wire coming in to the building from the main meter through a disconnect at the meter.

Do I need to bond the ground to the building itself?
 
To avoid these ads, REGISTER NOW!
OP
M

misterfixit

Well-known member
Joined
Feb 9, 2013
Messages
199
Location
Kaufman Texas
I was not clear, I apologize.

I have 2 ground rods at the building. Do both of them have to be connected to ground bars in panel?

Can one rod be bonded to metal, the other rod to the ground bar in panel?

Do both ground rods need to be bonded to the metal as well as the ground bars in panel?
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,439
Location
Minneapolis
Run a single continuous wire from one ground rod, to the next ground rod, to the ground bus in the panel. Run another single wire from the building metal to the ground bus in the panel.

Then of course, you connect the ground bus in the panel back to the main ground bus at the meter. The neutral bus is kept separate from the ground bus.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
I was not clear, I apologize.

I have 2 ground rods at the building. Do both of them have to be connected to ground bars in panel?

Can one rod be bonded to metal, the other rod to the ground bar in panel?

Do both ground rods need to be bonded to the metal as well as the ground bars in panel?

both rods need to go to the panel but not the metal on the building.

as said above use one continuous piece from rod to rod to panel

the building steel needs to be bonded to the panel, with a separate wire, as does any metal plumbing such as water and gas lines.
 