i'm about to get 8 400 watt bulbs and fixtures (110 volt) for my shop.. they came out of a warehouse... my question is: how many can i put on one 20 amp circuit??..
Be careful about making sure the voltage you have to work is one of the options your ballasts can use. In my experience 120 volt Metal Hallide lighting has been rarely used.
Advance or magnetek replacement ballasts that I've installed are 4.7 amps, I wouldn't load it more than 3 although I've seens lots of aplications where there are 4.I just looked at the spec sheet for a RAB 400w metal halide low bay, 4 amps @ 120v, so based on that -4 fixtures per circuit.
I wired mine on 3 different Edison Multiwire circuits. I pulled both hots and a neutral, split the tabs on the hot side of the duplex receptacles and pigtailed each receptacle (necessary by code on multiwire), used three 30amp double pole light switches (bought on clearance), labeled each half of the receptacle for which side of the circuit it was on, with a large red A and a large black B. 4 receptacles on each double pole common trip circuit breaker. I plugged in the lights alternating, A B A B. The fixtures I have were 120v ONLY and had come from one of several Sams or Walmarts in the Atlanta area that were converted to T8 fluorescents.
Charles
As noted, got them on a clearance. Home Depot often looks at inventory and if they have too much of something, it gets marked down temporarily to get the inventory down. These were Pass and Seymour and I paid about $4 each for them, thats cheap for 30 amp DP light switches.
I used 20 amp DP common trip breakers and 12 gauge wire.
Charles