I went outside and checked and it's a 100 amp breaker which is the main. Main breaker is on the meter box and the panel is in the garage around 40 feet from the meter.

Says 4 AWG XHHW-2 AL on the wire.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
that #4 should be protected with a 60a breaker supplying it.
 

twostory

Well-known member
Joined
Dec 23, 2005
Messages
554
Location
Duluth, Georgia

According to that chart (the cable manufacturer), you can run 110 amp thru that cable, if the cable is hanging in the air.

If it is in a race way, you only get 75 amp.

If it is buried in the ground (not on the chart) you may have a reduced current capacity.

The very cold soil in Alaska will help with the current capacity, since this cools the wire down. The wire has internal resistance, which will noticeably heat the wire when you run 100 amps thru it.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
According to that chart (the cable manufacturer), you can run 110 amp thru that cable, if the cable is hanging in the air.

If it is in a race way, you only get 75 amp.

If it is buried in the ground (not on the chart) you may have a reduced current capacity.

The very cold soil in Alaska will help with the current capacity, since this cools the wire down. The wire has internal resistance, which will noticeably heat the wire when you run 100 amps thru it.

Aluminum XHHW has a 75deg ampacity of 65 amps. 75 amps is from the 90deg column which can only be used for derating purposes. You cannot select your overcurrent protection based on ampacity from the 90deg column.

Once again, #4 AL needs to be protected by a 60 amp breaker in 99% of all cases.
 
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
It's protected by a 100amp breaker. Wired by an electrician so it's not anything I did.

The Wire runs in the attic I think. Meter box is outside the house on the bedroom wall and the panel is in the garage which is the opposite side of the house.

I would not think something that obvious could be done if it wasn't ok.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
It's protected by a 100amp breaker. Wired by an electrician so it's not anything I did.

The Wire runs in the attic I think. Meter box is outside the house on the bedroom wall and the panel is in the garage which is the opposite side of the house.

I would not think something that obvious could be done if it wasn't ok.

obviously that electrician didnt know what he was doing. I would replace that 100a breaker with a 60 asap, especially if its running through the house.
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
#4 aluminum with a 100amp breaker ain't going to happen on my property no matter who put it together. My garage has #2 copper with a 100amp breaker.
 
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
Not going to happen. House is spec'd to have 100 amp juice and that's what it will have. I might call in a sparky this week and get their opinion so I can use that to have the builder fix the problem.

obviously that electrician didnt know what he was doing. I would replace that 100a breaker with a 60 asap, especially if its running through the house.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Not going to happen. House is spec'd to have 100 amp juice and that's what it will have. I might call in a sparky this week and get their opinion so I can use that to have the builder fix the problem.


ahh, I didnt realize it was new construction.
 

hidollartoys

Well-known member
Joined
Jul 15, 2008
Messages
594
Location
K. C. Metro area
I have read and reread this post and it seems that the wire in question is actually a "feeder" as defined by the 2005 NEC code. Per Table 310.15(B)(6) pg 70-141 the wire size for 100 amp feeder is #2 al or #4 cu.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
I have read and reread this post and it seems that the wire in question is actually a "feeder" as defined by the 2005 NEC code. Per Table 310.15(B)(6) pg 70-141 the wire size for 100 amp feeder is #2 al or #4 cu.


That is Incorrect. 310.15 B 6 is for the service feeders that supply main power to a dwelling. A set of conductors supplying a sub panel cannot use the reduced sizes offered by that table.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I have read and reread this post and it seems that the wire in question is actually a "feeder" as defined by the 2005 NEC code. Per Table 310.15(B)(6) pg 70-141 the wire size for 100 amp feeder is #2 al or #4 cu.

That is Incorrect. 310.15 B 6 is for the service feeders that supply main power to a dwelling. A set of conductors supplying a sub panel cannot use the reduced sizes offered by that table.

He's right mrb. If that is the only lighting/appliance panel in the home, that feeder qualifies.

I went outside and checked and it's a 100 amp breaker which is the main. Main breaker is on the meter box and the panel is in the garage around 40 feet from the meter.

Says 4 AWG XHHW-2 AL on the wire.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
He's right mrb. If that is the only lighting/appliance panel in the home, that feeder qualifies.

I misinterpreted his post. I thought we were talking about a panel for the garage which was a sub panel coming off the main on the side of the house.

So this panel supplied with the #4 carries the entire load of the house? In that case, the #4 would need to be a #2 AL, but only if that panel its supplying carries the entire load of the house. If there is another breaker at the main which supplies anything on the house or attached garage then 310.15B6 is out for sizing that feeder.
 
Last edited:

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Its #4 al not CU

right, so per 310.15(B)(6) it would need to be #2 AL. Thats 2005. Is it conductors in conduit or is it cable? If its cable i think there is additional derating for SER if under 2008
 
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
It's the main panel which feeds the house/garage (attached garage).

The meter panel outside of the house has the main breaker (100 amp) and than the wire in question connects the meter panel to the main panel.
 
To avoid these ads, REGISTER NOW!

Schrodingers Cat

Well-known member
Joined
Oct 31, 2009
Messages
161
this is confusing:

is this the main feed for the house/garage?
or just a 100A feed from the service entrance to the garage alone?
is the SE overhead or underground?
is the wire from the meter box/100A CB to the garage panel in conduit?

my understanding:
SE into meter box (OH or UG)
meter box has a 100A Main CB
then the #4 Al goes from the meter pnl/100A CB to the main (and only) house/garage dist panel 125A (located in garage)

is this correct?
 

hidollartoys

Well-known member
Joined
Jul 15, 2008
Messages
594
Location
K. C. Metro area
this is confusing:

is this the main feed for the house/garage?
or just a 100A feed from the service entrance to the garage alone?
is the SE overhead or underground?
is the wire from the meter box/100A CB to the garage panel in conduit?

my understanding:
SE into meter box (OH or UG)
meter box has a 100A Main CB
then the #4 Al goes from the meter pnl/100A CB to the main (and only) house/garage dist panel 125A (located in garage)

is this correct?


Yes and garage is attached to dweling. Service disconnect and main panel are 40 ft apart. Wire is routed through attic.
 
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
Yes that's correct. Juice runs from the power company underground to the meter box on the side of the house and the main breaker, (which is 100amp) is there as well.

From the meter the wire in question (#4 AL) is used to get to the one and only breaker panel which is in the garage, about 40 ft from the meter.

It's not in conduit, just sheathed the same way Romex would be. 2 hots, 1 neutral and a ground wire. The pic of the grey wire shows what it looks like. (That wire is a "spare" #6 for the electric oven which I don't have)








this is confusing:

is this the main feed for the house/garage?
or just a 100A feed from the service entrance to the garage alone?
is the SE overhead or underground?
is the wire from the meter box/100A CB to the garage panel in conduit?

my understanding:
SE into meter box (OH or UG)
meter box has a 100A Main CB
then the #4 Al goes from the meter pnl/100A CB to the main (and only) house/garage dist panel 125A (located in garage)

is this correct?
 

Attachments

  • IMGP1299.jpg
    IMGP1299.jpg
    119.2 KB · Views: 97
  • IMGP1300.jpg
    IMGP1300.jpg
    138.6 KB · Views: 90
  • IMGP1302.jpg
    IMGP1302.jpg
    104.7 KB · Views: 87
Last edited:
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
I sent an email to the builder's agent with the info you posted. Do you have a copy of the page with the exact info I need? I searched on the web and can't see to find it. I'd rather not spend $75-80 for the code book just for this one thing.

"...The last concern is the feed wire from the meter panel outside the house
to the main panel. I pulled the breaker panel cover off in the garage to prep for painting the walls and I noticed that the feeder into the panel is #4 XHHW-2 Aluminum wire. It seemed small for 100 amp service, so I checked into it. Per the NEC (National Electrical Code) 2005 codebook, Table 310.15(B)(6) (pages 70-141), the wire size for 100 amp feeder should be #2 Aluminum OR #4 Copper. The #4 Aluminum wire is only rated for 65 amps. I'd like to know why #4 was used and how this can be legal since #2 is required by the NEC."


right, so per 310.15(B)(6) it would need to be #2 AL. Thats 2005. Is it conductors in conduit or is it cable? If its cable i think there is additional derating for SER if under 2008
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
i have the online nec, cant print or copy. Maybe someone else has the book and can scan the page for you.

that panel is a mess. Whats the jumper thing between the two neutral bars above the top two breakers? is it bare? Doesnt look factory. Wheres the factory jumper? I dont like how this passes across the two hot busses.
 
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
Panel isn't the neatest, but I have seen worse with "pro" jobs. As with anything, some people take more pride in their work than others.

The jumper is factory I think, I'm not sure. It's a Siemens panel. It has insulation on it, just hard to tell in the pic. It runs in front of the hots, about 3/4" away from them.

Bare copper is black a little from dust (cover has been off for a while) and also when I did the epoxy on my floor the acid didn't like the copper too much. The water pipes in the garage are like that as well.
Mistake I made not covering everything up, but I didn't know it would do that until after the fact, so not much I can do now.

It's not as bad as it looks in the photo, just the lighting makes it look like that.

No China drywall in the house, it's all made in the USA stuff.
 
Last edited:

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
ah ok. good you didnt end up with that drywall. I would clean the ends of and reterminate all the copper wires in that panel. An hour of work that could save a bigger headache later. Were the breakers installed when doing the floor which caused the corrosion? If so, I would replace any that carry a high load.
 

hidollartoys

Well-known member
Joined
Jul 15, 2008
Messages
594
Location
K. C. Metro area
Nate, maybe a call to your local codes inspection office is in order. If the house was given a certificate of occupancy then it might be something that needs to be addressed at the codes dept. management level. You might want to contact your insurance co to assist in your efforts. I believe the way it is now is wrong and should require a change. Just my two cents.
 
Last edited:
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
That #6 wire would feed the range if it the range were electric (both the range and dryer are setup for electric and gas).

I took a pic of it because the #4 feeder wire is the same type of wire.

I sent the builder's rep an email and I'll see how that goes. I have a 2 year "bumper to bumper" warranty plus a 10 year structural and so far they have been pretty good to deal with thankfully.
 

Giraffe

Well-known member
Joined
Jul 31, 2009
Messages
55
Location
TX
Nate, Maybe it is just the picture quality, but it sure looks like I see some copper strands coming out from the bottom of the main lugs in the second photo. I also see the AL on the neutral conductor. Is it possible that it is just the neutral that is AL and the other two are copper... or am I just seeing anti-oxidant paste?
 
Last edited:
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
Electrician is supposed to come by today to take a look.

I told him 125 amp breaker, #4 Aluminum and right away he said, HUH?? :shocking::wtf:

He wanted to know the timeframe it was wired so he can figure out who did the work. I was digging through paperwork a couple days ago and found that there was actually an electrical inspection done.... or... well signed off at least.

Futher proves my point that permits/inspections are a complete waste!
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Futher proves my point that permits/inspections are a complete waste!

Not all inspectors are clueless. You simply had a complete failure of the system.:mad: I'd probably look for contractor/inspector info on your permit label and bring it up to the local building dept. That's BS they wired your home that way and got away with it. You shouldn't be the one having to pay to fix it.

On the bright side, at least it looks like you found an electrician who seems to know what he's doing.
 
OP
N

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
I'm not paying for it, builder is covering it. For the most part - "If I'm not happy, they aren't happy"

Being that this is a fairly small town, I'm not going to press the issue about the inspection unless the electrician wants to do something about it.
 
Last edited:

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
glad to hear its getting straightened out. I dont know I would completely blame the inspector (although they should have caught this), as the electricians are the ones who are supposed to make sure they do their work to code. The inspectors cannot possibly catch every little thing, and they usually just have a laundry list of things they check for.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
The inspectors cannot possibly catch every little thing, and they usually just have a laundry list of things they check for.

This isn't every little thing. Verifying the incoming wire size should be one of the main items he looks for. Seeing tiny #4 AL landing on a 125 main should of been VERY OBVIOUS.

What's scary is how many other homes did this electrician wire for this builder the exact same way?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
What's scary is how many other homes did this electrician wire for this builder the exact same way?
I don't hang out a sign but on occasion get a call from friends, I can tell right away when the local "handyman" did the work to a place. Cut every ground wire off he come across. An Uncle called me a while back with water heater problem, I don't remember what was exact issue but the joker that replaced it snipped the ground wire off both ends of the cable. Went to another buds garage, same deal on every outlet and wires are now to short to re-use, gfci time. Did this to hundreds of things he worked on, just couldn't grasp the concept I guess and knew more than most people do about it, enough he never ask anyone WTF.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I am not a neat freak, my own panels got some strangled wire in them but I don't put both wires under the same screw thats for sure and make sure stuff is grounded and the bonds are in place.
 