4S & Handy boxes

To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
I prefer welded, but it really does not matter, handy boxes should NEVER be used and if considering using a handy box, place your hands on a anvil & have someone hit each finger 10 times with a hammer, after that then go ahead & use a handy box.

They are absolutely the worst type of box to use, and are a sure sign it was a DIY job.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,427
Location
Richmond, VA
I prefer welded, but it really does not matter, handy boxes should NEVER be used and if considering using a handy box, place your hands on a anvil & have someone hit each finger 10 times with a hammer, after that then go ahead & use a handy box.

They are absolutely the worst type of box to use, and are a sure sign it was a DIY job.

Why? What is better?
 

Fishingfoolemjak

Well-known member
Joined
Mar 21, 2017
Messages
176
Location
Sylva, NC
Sometimes a handy box is all that will fit, especially in custom job/locations. However, like stated above, avoid them if at all possible!
 

Fishingfoolemjak

Well-known member
Joined
Mar 21, 2017
Messages
176
Location
Sylva, NC
By “4S”, do you mean 4 square (or 1900’s)? If so, and you have room for a 4” square box, why would you look at using a handy box?
 

Hpozzuoli

Well-known member
Joined
Dec 11, 2013
Messages
3,428
Location
Rhode Island
What’s the problem with handy boxes? I use them all the time for just about everything. I have a milk crate full in my truck that comes with me from job to job. Just don’t bury them like any other box.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,442
Location
USA
con: Welded 4" boxes have sharper corners and edges.
con: You can break an edge weld by pounding on a stubborn knockout
pro: welded boxes are cheaper by a few cents in my area.

If I'm leaving the box exposed, normally I'll use a drawn box instead of a welded one because it's a smoother finish.
 

Hot Rod Grampa

Well-known member
Joined
Jul 7, 2017
Messages
812
Location
Near Cooperstown New York
Hard to believe anyone would post such an ignorant comment on the use of a handy box. There is nothing wrong when used in the correct application. Like anything else in this world, bad tradesmen can mess up the best equipment. Stupidity has no boundaries. Good grief.
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
I prefer welded, but it really does not matter, handy boxes should NEVER be used and if considering using a handy box, place your hands on a anvil & have someone hit each finger 10 times with a hammer, after that then go ahead & use a handy box.

They are absolutely the worst type of box to use, and are a sure sign it was a DIY job.

That's what you think of them, yet you have a preference? :lol_hitti:lol_hitti
 

Wirepuller

Banned
Joined
Oct 6, 2014
Messages
305
I prefer welded, but it really does not matter, handy boxes should NEVER be used and if considering using a handy box, place your hands on a anvil & have someone hit each finger 10 times with a hammer, after that then go ahead & use a handy box.

They are absolutely the worst type of box to use, and are a sure sign it was a DIY job.



Very ignorant statement. Half the time all the tamper and flow switches are installed so tight to other sprinkler fittings they're the best option.


Sent from my iPhone using Tapatalk
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,705
Location
Lebanon, TN
Hard to believe anyone would post such an ignorant comment on the use of a handy box. There is nothing wrong when used in the correct application. Like anything else in this world, bad tradesmen can mess up the best equipment. Stupidity has no boundaries. Good grief.

Grandpa,
Norcal is one of the most knowledgeable electricians on this board. His comment was a bit tongue in cheek, but he has a valid overall point. Handy boxes are a pain in the **** for anyone to work in or add anything to them. There are cases where one may have no choice but to use them, but in general terms they are a sign of less than quality work in many peoples opinion.

Respectfully, you need to spend a bit more time on this board and see the responses given by Norcal, he knows what he is talking about.
 
To avoid these ads, REGISTER NOW!

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,888
Why? What is better?

A handy box is 13 cubic inches. That is enough for a device and three 12 AWG wires. It is not enough for a device and four wires, so you can't use one for an outlet that has another outlet downstream, or for many other things. (which they're routinely used for, which is why they're the sign of a hack who doesn't know or care about wire fill rules.
 

Dagny

Well-known member
Joined
Jul 25, 2014
Messages
2,980
Location
Northern Wi.
What ya mean they are perfect for GFCI receptacles. I have a picture somewhere of one with 2 14-3s 3 14-2s and a SSU.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,427
Location
Richmond, VA
A handy box is 13 cubic inches. That is enough for a device and three 12 AWG wires. It is not enough for a device and four wires, so you can't use one for an outlet that has another outlet downstream, or for many other things. (which they're routinely used for, which is why they're the sign of a hack who doesn't know or care about wire fill rules.

Thanks. Admittedly, i have bought handy boxes for applications where based on this, i should have gone larger. I'll keep this in mind going forward.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Very ignorant statement. Half the time all the tamper and flow switches are installed so tight to other sprinkler fittings they're the best option.


They do have a place but it's very limited, I'll adimit to using them where they fit the application but when you see them used for more then 2 current carrying conductors & a receptacle it is a sure sign it was not well thought out.
 
Last edited:

markushofer27

Well-known member
Joined
Feb 4, 2012
Messages
114
The only good purpose I came across for a handy box is when lead I was working with on job used a hand box for a recept and 2 Mc going in it energized the steel,when he didn't bond xo to the frame on a step down when I told him it needs to be done several times.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Very ignorant statement. Half the time all the tamper and flow switches are installed so tight to other sprinkler fittings they're the best option.

All the tamper/flow switches I've ever seen (I've seen a lot of them in commercial) were hooked up with a section of flex conduit, and the boxes mounted on the wall.

flow2.jpg
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I prefer welded, but it really does not matter, handy boxes should NEVER be used and if considering using a handy box, place your hands on a anvil & have someone hit each finger 10 times with a hammer, after that then go ahead & use a handy box.

They are absolutely the worst type of box to use, and are a sure sign it was a DIY job.
Exactly!:thumbup::thumbup::thumbup::thumbup:
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I'll take a 4sq box with a plaster ring any time possible over a handy box.
I come across handy boxes on side of furnaces all the time,there's room for a 4sq box 99% of the time on a furnace,some contractors are just concerned about saving $.50 over price of a 4sq is all.
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
What time is the Banned Wagon leaving tonite?

Holy smokes. Over the size of an electrical box?

I just used a couple putting some lights in my shed. One for a switch, one duplex outlet on the ceiling. I have 14/2 NMD-90 in conduit coming from my garage to the switch, then on to the duplex outlet. For those that don't like these, what should I have used?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,873
Location
NJ
Holy smokes. Over the size of an electrical box?

I just used a couple putting some lights in my shed. One for a switch, one duplex outlet on the ceiling. I have 14/2 NMD-90 in conduit coming from my garage to the switch, then on to the duplex outlet. For those that don't like these, what should I have used?

Using conduit where handy boxes are at the end of a run is usually fine.

Observing conductor fill is usually the violation when running cable and daisy chaining from box to box and also putting devices in the same box, the fill is exceeded. I always hated handy boxes b/c I had to search for a shorter screw for devices - reason for my first bolt cutter.

Even if done correctly at initial install, someone always needs to add to a ckt and rarely changes out an existing handy box to a larger box.

A 4" sq x 1-1/2" (or even 2-1/8") deep is usually the smart choice so there is plenty of room to wire it up initially and go back into and add on if needed.
 