50 amp breaker as main.

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Seems to me I read here that you can use a regular breaker as a main. I have a buddy who is wiring a large storage shed. He ran wire to the building 2-2-2 I believe. He got a Square D homeline 100 amp box but didn't get a main, he is only going to have two circuits, one for lighting ad one for 6 outlets. I have a 50 amp Homeline Square D breaker, can that be used as the main and be code compliant?
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Yes it can with a hold down kit but what is the second panel? A 100 main lug and how many spaces? If this is a common 6 space ( yes,,,,,,,,,,,,, I know more details for code police ) but with only 2 breakers can be wired main lug and doesn't need a main. Especially applicable for these 2 minor circuits as there is absolutely no potential for overloading it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
Yes u can use a regular breaker to back feed the panel as a main disconnect but u will need a hold down screw/kit.

However, unless theres more than 6 breaker handles, then a main disconnect isnt required. U said theres only 2 circuits...

Also, if your friend for sure used 2-2-2 then it needs to be changed to a 4-wire feed as 3-wire feeds are no longer allowed....

He will also need 2 ground rods and the neutral bus needs to be isolated. He may need to purchase a separate ground bar kit.
 
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Thanks for the quick response. If he ever does expand the system he can put a main in at that time.
 
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
He has the two ground rods in and he just confirmed the wire is 2-2-2-4. The breaker box came with the neutral isolated

Thanks
 
To avoid these ads, REGISTER NOW!
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
You guys deserve the credit, I work with this guy and over the years we have helped each other with lots of buildings and building projects. He decided to put up a 26 x 30 storage building last summer and asked me about getting power to it. I sent him an e-mail of the sub-panel diagram that you and others have posted. It really is a great reference and explains things very well.
 
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
About 75' I think, I put the overhead door in for him a couple of weeks ago and that's what I would guess.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
With #2 WHY waste all that potential amperage by limiting it to a 50A breaker??? Just because you happen to have one??
A 2-pole HOM is like $12. Get an 80 or 90A.

*Edit - OK, so an 80 or 90 is like $40. A 50 or 60 is like $12. Still silly to waste that large #2.
 
Last edited:
OP
D

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
If I remember right I think a buddy of his who works for the power company gave him a good deal on some. He also wanted to get lights on that day and he would have had to go 45 miles out of his way to get a main.
 
Last edited: