50 Amp circuit breaker , time delay ?

padronanniversary

Well-known member
Joined
Jul 11, 2010
Messages
1,367
Location
Minesooooooota
Looking for some help on a question. I was reading the input requirements on a Miller252 and say that is wanted a 50Amp time delay fuse or time delay breaker.

I have never seen a time
delay or slow blow type breaker.

Can anyone recommend a 50 Amp breaker for 230 for an application like a ESAB 280 or Miller 252 ? Also is this something I can get at home depot or lowes ?:shocking:

I'm trying to get everything all wired up beforehand.

Thank you in advance !!
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
just get a normal breaker (the correct make and model for your panel) and you will be fine. All normal consumer breakers are time delay.
 

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,273
I've read that a 60amp is an exceptionable substitute. Any 50amp will work fine.
 
Last edited:
To avoid these ads, REGISTER NOW!

Flange

Well-known member
Joined
Jun 9, 2010
Messages
424
Location
Northern England
All circuit breakers are rated for the time it takes to break the circuit. An electrical engineer will design a circuit for a particular application and specify what spec breaker to use.

Most common circuits, say for a domestic situation, will be covered by standard breaker for that situation. For anything else then ask someone who knows.
 
OP
P

padronanniversary

Well-known member
Joined
Jul 11, 2010
Messages
1,367
Location
Minesooooooota
typically fuses have blow curve characteristics. I would assume a breaker has similar; both of which are based on current and time, not just time.
 