hello. iam running my welding receptacles in my new shop and will have 2 places to plug in my welder. I am using 6 gauge wire with 50 amp receptacles with a 50 amp breaker. I will only be using 1 receptacle at a time. Now my question. since I am running both of these off of the same circuit I need to wire into one receptacle then back out to go to the other further down the shop wall. My problem is that the #6 wire is too big to put 2 blacks and 2 whites into the receptacle. Has anyone else ran into this and what did you do to make it work? Thanks.
 
To avoid these ads, REGISTER NOW!

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
First of all, this is not Kosher. But if you must do it, pigtail your connections at the first box with clamp connectors. Make sure to get a big enough box.

Any reason to not just do one and use a beefy extension cord?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Proper way to do this is make sure to have a j box deep enough to do pig tails and splices. Splice in short pieces of wire to connect to the outlet. U will need blue wire nuts.

However, some AHJ disallow more than 1 240v outlet on the same circuit so u should check to make sure your AHJ doesnt have any rules against this...
 
OP
B

BFalfa

Well-known member
Joined
Nov 24, 2012
Messages
105
The reason for the 2 outlets is that my shop is 40x72. 1 outlet is in my "shop" area and the other is in the middle of the building incase I need to move my welder to that location for a repair. However I do plan to use a beefy extension cord at that receptacle. Thanks guys.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Proper way to do this is make sure to have a j box deep enough to do pig tails and splices. Splice in short pieces of wire to connect to the outlet. U will need blue wire nuts.

However, some AHJ disallow more than 1 240v outlet on the same circuit so u should check to make sure your AHJ doesnt have any rules against this...


Blue wire nuts are only listed for (2) #6s maximum. In the case of a pigtail it will not work. You'd need to use Polaris connectors or split bolt connectors.

It doesn't matter what the AHJ disallows. The AHJ has to follow the Code.
Unless there is a local amendment to the Code, in writing, they aren't allowed to disallow anything.

The NEC has absolutely no rules against it, and the IEC allows multiple receptacles on 240V circuits to 20 Amps.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
you would be much better off running two separate circuits for this. to make this splice and house the receptacle in a box will require at least a 4 11/16 deep box and even that my be too small. then you are looking at having a separate jbox for the splice and dropping into the device box from there. this is one of those times where you don't want to pass over dollars to save dimes
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If you havnt bought the wire yet use number 8. What machines do you have? The only ones that come with a factory cord that require 8 are some 250 class migs and even then those are in real welding shops where they may use special gas screaming wide open,,, even then they need to change the guns that come on the units. A 250 will never warm a 10 running 035/c25 and will run the buzzer class stick machines.
If you are using 10 though no putting multiple outlets on a circuit.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
B

BFalfa

Well-known member
Joined
Nov 24, 2012
Messages
105
I actually do already have the wire ran. thanks for all the help. I think I have it figured out.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Blue wire nuts are only listed for (2) #6s maximum. In the case of a pigtail it will not work. You'd need to use Polaris connectors or split bolt connectors.

It doesn't matter what the AHJ disallows. The AHJ has to follow the Code.
Unless there is a local amendment to the Code, in writing, they aren't allowed to disallow anything.

The NEC has absolutely no rules against it, and the IEC allows multiple receptacles on 240V circuits to 20 Amps.

thats what I meant. Didnt have time to spell it out!

And the OP is using outlets higher than 20a...
 
OP
B

BFalfa

Well-known member
Joined
Nov 24, 2012
Messages
105
well...I had to look up what AHJ meant and have no idea what the NEC is..so call me dumb. Iam in the middle of nowhere Midwest.. although I am able to do pretty much whatever I want to on my property, I do try to do things the right way. :)
thanks again guys.
 

Grinder Bill

Well-known member
Joined
Jan 11, 2011
Messages
217
I recently bought 5 100A splitters to do much the same thing. Paid $35 each, new. Ace APS100

SplitterBoxesType3R-2hole.jpg


http://www.acemfg.com/commercial-enclosures.html
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
well...I had to look up what AHJ meant and have no idea what the NEC is..so call me dumb. Iam in the middle of nowhere Midwest.. .


You're not dumb by any stretch of the imagination. Just the fact that you're here asking questions proves that. ;)

Since you still seem to be vague on your location, here is the list of States, together their various Electrical Codes.

http://www.mikeholt.com/necadoptionlist.php

You're still subject to local Codes though. The best way to check is with through the local building department.
 