Good move, for all sorts of reasons.
No. It's based on the concept of "duty cycle"; "jeremy v" explained it perfectly.
That said, just because you CAN "get away with" undersized wiring on a dedicated welder circuit, that doesn't mean it is necessarily a good idea to do so. The welder you're running off that undersize wiring will still be subject to such things as the voltage drop imposed over the length of run (which will be more severe at shorter distances, the lighter the wiring is), and therefore perhaps not perform to it's peak potential (tho' whether you'd notice the difference in any particular scenario is at least debatable, and will depend on the specific details of that scenario). And besides, someday you may want to use that circuit for something other than a stick welder -- ooops!
NO WAY that 10/3 is good for 50+ amps.
Extension cords are not subject to the same "rules" as permanently installed wiring; but that doesn't mean that common sense should be thrown out the window. Per the NEC, AWG 10 wiring is good for 30-40 Amps, depending on the specific type of wiring and the temperature rating of its insulation. Normally, the lower limit applies.
Extension cords are generally limited to lower maximum currents than permanently installed wiring, in part because they are routinely subjected to wear, tear and general abuse, and thus must be presumed to be somewhat degraded in the field.
Compare your "home brew" cord to:
http://www.homedepot.com/p/Tasco-50...d-Yellow-with-Black-Stripe-05-00118/203534037
and note: "Maximum Amperage (amps) 15 A"
Now, I might reasonably push things a LITTLE further than that (perhaps 20-30A), if I had the need; but certainly not to anything like 50 Amps.
Also, the very fact that it is an extension cord means the effective length of the wiring run is being extended, and thus voltage drop becomes more of an issue. Running 50 Amps through a 50 foot AWG 10 extension cord will impose about 6.2V of drop just in the extension cord itself, before any of the wiring leading up to the receptacle that cord is plugged into is even considered. At 240V, that's "edgy" at best; at 120V, it is grossly excessive.
Well... Not exactly. But for practical purposes, that's probably not a horrible way to think about it. I'd still be nervous about 50A, tho', even for that application.
YUCK!
That page is an absolute travesty of misinformation, "voodoo engineering", and inappropriate sweeping generalizations. You should ignore it entirely. By the author's own admission, the information on load carrying capacities is third-hand; and he even goes on to further waffle with statements like "the rated ampacities are just a rule of thumb." In short, it is simply NOT a credible reference.
And BTW, "chassis wiring" refers to 12VDC automotive wiring -- not exactly what we're dealing with here!
Actually, that would be for permanently installed wiring, which is not subject to the various additional issues which affect extension cords.
As discussed above, that's a special case.
Not a good idea. What exactly are you planning to run off this home-brew cord? If it is a relatively light load, fine. But I certainly would NOT recommend you even attempt to draw anything like 50 Amps through it, even in short bursts.
We live to serve.
Well, that much is good anyway. "SJTW" stands for:
Code:
S = Service Grade
J = Hard Service
T = Thermoplastic
W = Outdoor (sunlight resistant jacket and
wet location rated conductors)
.
Or, in something approximating English: That type rating means the cord is generally suitable as an outdoor extension cord.